Results 1 to 15 of 15
02-03-2010, 06:03 PM #1
Liebert Hiross Close Control Humdifier bottles
Hi All
I am going to replace a leaking faulty humidifier bottle in a close control liebert hiross unit.
The model of the indoor is: M350A001V102002PO
My question is what is the procedure for replacing these.
Is there a PCB board with a dip switch to drain down or is it done from the controller.
The controller is situated on unit 1 where the problem is and controls 4 units in total.
many thanks lee
02-03-2010, 07:24 PM #2
Re: Liebert Hiross Close Control Humdifier bottles
Lee, haven't found your model number, didn't look too deeply, but have a look on the Liebert site, there are manuals for downloading etc; you might find something close.
The one I read said push the drain button, so probably not your model
http://www.liebert.com/Default.aspxBrian - Newton Abbot, Devon, UK
02-03-2010, 07:31 PM #3
wrong post
02-03-2010, 07:44 PM #4
I look after a few Liebert close control units but they're all trend controlled, not hiross. On these the humidifier controller is a carel pcb. On these the way i drain down is link 2 terminals at the top of the board marked DR and GND.
03-03-2010, 08:12 PM #5
Hi brian
Had a look could not find the unit on there
coolandlew, will have a look next time on site see if they have a carel pcb thanks for your input
anyone else know ?
09-03-2010, 09:33 AM #6
pleasure to meet u,i have problem with liebert aircond.if u know about LIEBERT model cm 50 af.how the sequencing setting/configuration.can u help me...
09-03-2010, 06:48 PM #7
if it has the standard interface then scroll down until the screen say "dr" then press the enter button, it will probably say off change to on and it will energize the drain solenoid. Keep doing this until the cylinder is empty, no password is required.
11-03-2010, 07:24 PM #8
hi all
changed the bottle today, on the controller there is a setting
the setting is DRAIN which was off, set to on and did this a few times.
however the bottle had not drained as i found when removing it. Strange that it did not drain
tested the bottle and it reached its setpoint and noticed water level had decreased from the point where the water had first filled.
cheers lee
24-03-2010, 09:11 AM #9
Hi Abov,
What do you want to sequencing setting/configuration for CM 50
30-03-2010, 10:40 AM #10
sounds to me if u had issues manually draining humidifier bottle via controller and this was done correrctly drain solenoid may be faulty be careful this can cause problems with humidifier bottle aswell as if water keeps draining or vice versa cannot drain causes issues with heater elements in bottle
30-03-2010, 07:41 PM #11
hi tradybrad
will keep that in mind, i have never used the liebert hiross controllers and found them to be non user friendly, i was fairly certain that the drain ON feature i selected was correct.
I noticed the Water level in the bottle had decreased quite a lot which i felt it may have drained but to be honest i could not be sure.
cheers
lee
31-03-2010, 05:34 PM #12
Scroll down menu to drain, set to on, ( no pass word required) drain soleniod valve will open for 30 seconds and then reset.
31-03-2010, 08:42 PM #13
hi there yes thats the setting i did, its says in the manual to set to ON a few times i think. I followed this command but still had not drained down.
04-04-2010, 07:29 PM #14
Moondawn,
Check soleinod valve coil, 240v etc when activated,also can be blocked with gunge etc.Also cylinder looks like it has water in, make sure it has.
Jim
08-08-2010, 08:00 AM #15
Several month ago I found a digtial out pin damaged on Hiross controller board, so the drain function of the humidifier is not useful (even if the drain in manual setting page is ON).
It's too expensive to replace the whole board. Then I have to DIY the circuit by adding a cicular dual time delay relay to control the drain time and the interval time automatically.
Airedale Close Control Service and Technical Manuals?
By Mozambezi in forum Air ConditioningReplies: 5Last Post: 03-02-2011, 09:39 PM -
Mitsubishi Close Control
By techni in forum Air ConditioningReplies: 5Last Post: 16-02-2010, 09:39 PM -
Leak on Airedale Close Control, Help!!
By Bash1803 in forum Air ConditioningReplies: 19Last Post: 29-09-2009, 09:23 AM -
wall mounted close control
By dannycool in forum Air ConditioningReplies: 15Last Post: 25-01-2009, 07:36 PM -
Hiross Hirange Close Control Unit
By garyjh24 in forum Air ConditioningReplies: 1Last Post: 06-05-2008, 10:07 PM