    Hi All,

    I have to calculate cooling load for a computer lab which contains 1 UPS of 15 KVA and 30 numbers of SMF Battery (100 AH). (They are keeping the UPS and Batteries inside the lab for security reasons)
    How to calculate load for these?
    Please help

    Regards

    Jacob



  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Air conditioning load calculation

    Quote Originally Posted by ejacob View Post
    Hi All,

    I have to calculate cooling load for a computer lab which contains 1 UPS of 15 KVA and 30 numbers of SMF Battery (100 AH). (They are keeping the UPS and Batteries inside the lab for security reasons)
    How to calculate load for these?
    Please help

    Regards

    Jacob

    Provide some details
    · Lab length, width, height.
    · Ups electrical wattage
    · Number of people
    · Electrical lighting wattage
    · Peak load Ambient temperature
    · Whether lab conditioned space or unconditioned space.
    · Wall area and exposure side

    moideen-dubai

  3. #3
    Join Date
    Dec 2007
    Location
    Hereford
    Age
    65
    Posts
    8
    Rep Power
    0

    Re: Air conditioning load calculation

    Making the assumption that the 15 kVA UPS is actually powering the computer equipment in the lab you are looking at 15 kW of heat gain (in round numbers) from the computer hardware.
    The UPS itself will chuck out around 10% of its rated load as heat so that's another 1.5 kW.
    Assuming again that the lab is not more than 50 sq.m, I would suggest 20 kW sensible cooling required.

  4. #4
    Join Date
    Mar 2010
    Location
    guangzhou
    Posts
    7
    Rep Power
    0

    Re: Air conditioning load calculation

    need some more details:
    the actual using building area
    how many rooms the ambient temp
    ^_^

Similar Threads

  1. Product Load Calculation
    By boy in forum Commercial
    Replies: 4
    Last Post: 12-08-2008, 02:50 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Cooling Load Calculation
    By jervame_sireh in forum Fundamentals
    Replies: 0
    Last Post: 21-04-2007, 11:05 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •