    Thumbs up return air , please help me,!!!



    Hi, friends !!!
    i have an room which just need 18000 btu/h !!!
    But i use 21000 btu/h .
    Now i have problem , the temp is alway lower than the set temp !!! (ex: i set temp at 23 the room temp will be 21 ) so,can i fix this problem ???
    Thank , a lot my friends !!!
    Thank forum and best development !!!



  2. #2
    Join Date
    Feb 2008
    Location
    QLD
    Age
    53
    Posts
    74
    Rep Power
    17

    Re: return air , please help me,!!!

    Set 25 ;-)

    If it is an inverter then most units will go to lowest running power, for one degree past set point, before switching off. Best option is to set a slightly higher temp.

  3. #3
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: return air , please help me,!!!

    Hi your rating of your AC is just a number at one point, you may be getting more or less depending on many factors.
    I would say just turn up thermostat by 2C (it may just be a calibration issue) When testing control temps you must have thermometer in the same place as AC thermostat sensor.
    If AC is way to big, you tend to find the the room will have very high RH.

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: return air , please help me,!!!

    Also, set the fan to its lowest speed.

  5. #5
    Join Date
    Jan 2010
    Location
    Viet Nam
    Posts
    18
    Rep Power
    0

    Re: return air , please help me,!!!

    thank friend !!!
    the sensor of remote and return air is the same at the temp set in remote . but the temp of room is lower than 1.5 to 2 deg !!!
    Thank friends
    thank forum and best regard !!!

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: return air , please help me,!!!

    If the return air is warmer than the room it is because the return has picked up the load from the room.

    More details as to the type, location and airflow around, from and back to the unit would be useful.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Jan 2010
    Location
    Viet Nam
    Posts
    18
    Rep Power
    0

    Re: return air , please help me,!!!

    Hi, friends !!!
    After have a full tracking with my VRV3 system i have some parameter :
    -The set temp = 23 deg (the temp want to set for the room)
    - the return air temp = 23 deg
    - the remote sensor temp = 23 deg

    - The temp of room = 21.5 deg ????
    What were happen ?
    our group had tried our best to fix this problem ....
    ex :- setting to use only remote sensor
    -change remote position
    -check all the sensor
    but it seem not have any effective .
    Could you hep me , my friends?
    Thank you a lot .
    Thank our forum .
    Best Kind !!!

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: return air , please help me,!!!

    Whereabouts is the remote controller in relation to where you are measuring the room temperature?

    What happens to the room temperature when to increase the control temperature by 2 degrees?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Jan 2010
    Location
    Viet Nam
    Posts
    18
    Rep Power
    0

    Re: return air , please help me,!!!

    hi, friend !!!
    Have a nice day (^_^)
    thank you for your advice
    when i set the time of room = 24 deg
    The remote sensor temp = 24
    the return air sensor = 24
    And the temp of room is maintain at 22-22.5
    Thank you a lot !!!
    thank forum
    Best kind and best regard

  10. #10
    Join Date
    Jan 2010
    Location
    Viet Nam
    Posts
    18
    Rep Power
    0

    Re: return air , please help me,!!!

    oh, friends !!!
    Why you do not help me ?
    I am tire so much for that problem
    who can give me an advice ???
    Thank you alot
    thank forum !!!
    Best regard !!!

  11. #11
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: return air , please help me,!!!

    Quote Originally Posted by vietvho View Post
    oh, friends !!!
    Why you do not help me ?
    I am tire so much for that problem
    who can give me an advice ???
    Thank you alot
    thank forum !!!
    Best regard !!!

    Your main problem is that the A/Cis to big for the area being conditioned keep setting the temp higher till you are happy

    Toosh
    My wife used to say you never listen to a word I say at least I think that what she said

  12. #12
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: return air , please help me,!!!

    The unit is over sized. Not only temperature will go down humidity also will increase. Best thing is to change the air quantity to suit your requirement then the thermostat can take over to modulate within a range.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: return air , please help me,!!!

    With what instrument you are measuring that temperatures? Is it calibrated?
    Or you are giving us temperatures of unit thermistors read from remote control and actual room temperature read from some measuring instrument.

    It looks to me that your measuring instrument is off by 1.5°C
    Last edited by nike123; 13-03-2010 at 04:39 PM.

  14. #14
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: return air , please help me,!!!

    Turn the fan speed down to the LOWEST you can select. This will mean less air circulation so less output from the unit.

    particulary useful if the unit is oversized.

Similar Threads

  1. daikin return air problem
    By Kev The Tool in forum Air Conditioning
    Replies: 7
    Last Post: 17-02-2010, 03:50 PM
  2. McQuay ALS F XE273.2 990Kw, highest return temp?
    By THE WOMBAT in forum Technical Speculations
    Replies: 1
    Last Post: 07-08-2009, 10:59 AM
  3. Best place for return air sensors, in the room or ceiling void?
    By back2space in forum Air Conditioning
    Replies: 27
    Last Post: 06-07-2009, 06:21 AM
  4. R404a Oil Return
    By dallan in forum Industrial
    Replies: 1
    Last Post: 23-08-2004, 12:40 AM
  5. return air
    By subzero*psia in forum Air Conditioning
    Replies: 1
    Last Post: 12-07-2001, 04:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •