    C&G 2079 Training



    Having recently taken the 2079 exam and practical.
    With several of my colleagues.
    We were all slightly shocked by the response of our very experienced trainer.
    Basically when being questioned on charging technique of a Zeotropic (Blend) Refrigerant.
    Where as Chiller Engineers we are taught to charge with Vapour ( throttle the liquid prior to it entering the system).
    Until reaching a system pressure compatible with 0c.
    Therefore eliminating the possibility of creating ice crystals within the condenser or evap.
    Our instructor was having none of it
    We have all discussed this before I know, and it's irrelevant for a lot of the guys!
    But at least if you are informed of it's relevance, it can be applied when necessary.

    Has anyone else come across this during training?
    Grizzly



  2. #2
    Join Date
    Jan 2008
    Location
    uk
    Posts
    13
    Rep Power
    0

    Re: C&G 2079 Training

    come on grizzly the trainer knows best dump all the liquid in and whalst your at it turn the water pumps off lol

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: C&G 2079 Training

    Quote Originally Posted by Lman View Post
    come on grizzly the trainer knows best dump all the liquid in and whalst your at it turn the water pumps off lol
    You been there too I guess?
    Grizzly

  4. #4
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: C&G 2079 Training

    I suppose it could just be a misunderstanding. We still charge in the liquid state but allow to vaporise before entering the system, until as you say above oc saturated. However you would hope he could have realised that.

  5. #5
    Join Date
    Jan 2008
    Location
    uk
    Posts
    13
    Rep Power
    0

    Re: C&G 2079 Training

    No he did mean dump it in as liquid as we told him we throttle it back to prevent icing. The reply was basically why would you want to do that use the vac to get as much liquid in as you can.

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: C&G 2079 Training

    So long as it leaves the bottle as a liquid it doesn't matter what state it enters the system, and as you say Grizzly it wants to be a vapour till the saturation (? i forget the propper terms ) temperature for the refrigerant is above the freezing point of what you is chilling.

    And if you are putting the whole bottle in you can take it out as vapour also, as it'll get mixed up again in the system.

    Jon

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: C&G 2079 Training

    Hi Jon.
    thanks for the input. as I say we have all discussed it before, it was just that Our instructor was not interested.
    After all no-one is going to argue with their assessor are they.
    Yet they are only human like the rest of us.
    It's no big thing I was just wondering as to whether anyone else has experienced similar.

    Thanks for the back-up Lman.
    Grizzly

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: C&G 2079 Training

    I think also Grizzly that some people, your assessor eg, sometimes listen but don't hear what is being said.

    He has to ensure that his trainees take liquid out of the bottle and that is what he will stick with.

    If you add complications like doing it properly then you simply confuse the issue. Some people haven't grasped yet that you can use your manifold valves as throttling devices thereby splitting the phases at that point.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: C&G 2079 Training

    Quote Originally Posted by Grizzly View Post
    Having recently taken the 2079 exam and practical.
    With several of my colleagues.
    We were all slightly shocked by the response of our very experienced trainer.
    Basically when being questioned on charging technique of a Zeotropic (Blend) Refrigerant.
    Where as Chiller Engineers we are taught to charge with Vapour ( throttle the liquid prior to it entering the system).
    Until reaching a system pressure compatible with 0c.
    Therefore eliminating the possibility of creating ice crystals within the condenser or evap.
    Our instructor was having none of it
    We have all discussed this before I know, and it's irrelevant for a lot of the guys!
    But at least if you are informed of it's relevance, it can be applied when necessary.

    Has anyone else come across this during training?
    Grizzly

    Could it have been a misunderstanding.

    I tell people to bomb charge the refrigerant in,
    all of it in one go if possible but if the pressure equalises
    then the refrigerant has to be bled in while the system is running.

    On the assessment you have to demonstrate both liquid
    charging to the system and bleeding the stuff in to a working system,
    so is it possible the guy was just concerned with that more and lost
    the point of your argument??

    I know what you mean about questioning the assessor but they are only
    human and don't know it all.

    I know I don't

    taz.

  10. #10
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: C&G 2079 Training

    Something i thought was wierd. A question come up something like although cant remeber the exact wording "what should R410 gauges NOT have". The answer they were looking for was a sightglass, however on my next visit to NRS there on display was a Rothenburger display stand full of different gauges and the 410 one's DO HAVE sightglasses !!!!!!

    Work that one out

  11. #11
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: C&G 2079 Training

    Quote Originally Posted by Latte View Post
    Something i thought was wierd. A question come up something like although cant remeber the exact wording "what should R410 gauges NOT have". The answer they were looking for was a sightglass, however on my next visit to NRS there on display was a Rothenburger display stand full of different gauges and the 410 one's DO HAVE sightglasses !!!!!!

    Work that one out
    yes heard that,mine have a sight glass you ask yourself do r410 systems have sight glass fitted?

  12. #12
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: C&G 2079 Training

    Quote Originally Posted by Latte View Post
    Something i thought was wierd. A question come up something like although cant remeber the exact wording "what should R410 gauges NOT have". The answer they were looking for was a sightglass, however on my next visit to NRS there on display was a Rothenburger display stand full of different gauges and the 410 one's DO HAVE sightglasses !!!!!!

    Work that one out
    That's mainly relating to people using their manifold set for pressure testing.

    Yes, the manifold should take the test pressure but, is it worth the risk?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. C&g 2079
    By frank in forum Training
    Replies: 184
    Last Post: 19-11-2012, 06:29 PM
  2. Replies: 17
    Last Post: 20-10-2010, 08:37 AM
  3. U.K. Training Ref C&G 2079 and ACRIB?
    By Grizzly in forum Legal-Business-Marketing
    Replies: 32
    Last Post: 24-04-2010, 09:31 AM
  4. c&g 2079
    By farren in forum Training
    Replies: 6
    Last Post: 07-05-2009, 04:23 PM
  5. Lack Of Training Centres
    By Latte in forum Training
    Replies: 12
    Last Post: 06-11-2008, 02:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •