    Exclamation Three questions about expansion valves



    Hello

    1 - Do TEV's (internally or externally equalised) have to be fitted on a horizontal pipe or can they go on the vertical? If so, can the bulb go on the vertical?

    2 - What limits the distance between the TEV and evaporator inlet? (Without changing the design)? Would 500mm on a typical cellar cooler be ok for example?

    3 - Is it ok to use reducers either side of a TEV?

    Thanks.
    Last edited by Contactor; 27-02-2010 at 07:21 AM. Reason: to add third question



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Three questions about expansion valves

    Three questions but only two numbered, you're trying to trick us

    Quote from the Sporlan documents on TEV...
    TEVs may be mounted in any position, but they should be installed
    as close to the evaporator as possible.

    Have a read up on their literature, there is a lot that can be learned from them, I know I do.

    http://www.sporlanonline.com/literature.shtml
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Three questions about expansion valves

    thanks brian

    third quetion now added, apologies

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Three questions about expansion valves

    In most split and multisplit systems, the expansion valve is in the outdoor unit, so....
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Three questions about expansion valves

    This is for a lu-ve cellar cooler and two lu-ve cabinet evaporators. Lu've instructions say the TEV should be directly onto the distributor and that the bulb has to be 500mm away, but I don't have room.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Three questions about expansion valves

    Quote Originally Posted by Contactor View Post
    This is for a lu-ve cellar cooler and two lu-ve cabinet evaporators. Lu've instructions say the TEV should be directly onto the distributor and that the bulb has to be 500mm away, but I don't have room.
    There's your answer.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Three questions about expansion valves

    Hey Peter,

    yore wright to, but this is because the are reverseble heating/cooling.....yes?

    Ice

  8. #8
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: Three questions about expansion valves

    Quote Originally Posted by icecube51 View Post
    Hey Peter,

    yore wright to, but this is because the are reverseble heating/cooling.....yes?

    Ice
    Also most of the 'Only Cooling' types have the expansion device (capilary or valve) in the outdour unit. Main reason : noise limitation in the indoor unit.

  9. #9
    Join Date
    Feb 2009
    Location
    bruges
    Age
    45
    Posts
    42
    Rep Power
    0

    Re: Three questions about expansion valves

    noise limitation in the indoor unit = true

    tip : always check the way the bulp or sensor is connected to the tube. (this could save compressor lives )
    Last edited by frederik79; 03-03-2010 at 06:05 PM.

  10. #10
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Three questions about expansion valves

    Quote Originally Posted by Contactor View Post

    2 - What limits the distance between the TEV and evaporator inlet? (Without changing the design)? Would 500mm on a typical cellar cooler be ok for example?
    Danfoss says that maximum distance between TEV and evaporator ilnet would never been more than distance equal 7 diameters of connected liquid pipe.
    In some places will have to think ...

  11. #11
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Three questions about expansion valves

    Quote Originally Posted by Contactor View Post

    If so, can the bulb go on the vertical?
    Yes it can be...but usually it place in horizontal pipe...
    In some places will have to think ...

  12. #12
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Three questions about expansion valves

    Quote Originally Posted by Aik View Post
    Danfoss says that maximum distance between TEV and evaporator ilnet would never been more than distance equal 7 diameters of connected liquid pipe.
    By evaporator inlet did you mean distributor?

  13. #13
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Three questions about expansion valves

    Quote Originally Posted by nike123 View Post
    By evaporator inlet did you mean distributor?
    Yes, distributor.
    In some places will have to think ...

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Three questions about expansion valves

    Quote Originally Posted by Contactor View Post
    1 - Do TEV's (internally or externally equalised) have to be fitted on a horizontal pipe or can they go on the vertical?
    When you installing TXV on evaporator with distributor, place valve exit vertically (preferably downward) in order that gravity has no influence on equal distribution of liquid refrigerant.
    Last edited by nike123; 09-05-2010 at 09:14 AM.

  15. #15
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Three questions about expansion valves

    Presumably Danfoss are saying that because they have to have something to design to rather than being essential. Also pointing it downwards on the vertical would be under ideal conditions.

    I suppose if you have it one metre away at an angle it will still do the job, right?

  16. #16
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Three questions about expansion valves

    If you have some distance between TXV & distributor, try to make the elbows - if any - as large radius sweeps. What most of the literature is really bleating about is trying to keep the 2-phase fluid as a mixture rather than have it separate into a liquid only & vapour only stream. This could make the distributor's life a little more tricky.

    Noise can also become a bit of an issue with long lengths plus elbows between TXV & distributor.

    Can you do it? Yes, sure - it works, as long as you are careful. If it didn't, then how on earth do the TXV's in outdoor units get the job done? How many techs bother overly with the 2-phase line between outdoor unit & indoor evap?
    Last edited by desA; 07-06-2010 at 06:27 PM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  17. #17
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Three questions about expansion valves

    Bulbs ideally on horizontal, you can use reducers either side of the valve, can you place even a short piece of pipe vertically into the distributor? I've stuck valves externally to rooms especially where space is tight.

    alec

Similar Threads

  1. electronic expansion valves
    By bill1983 in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 23-02-2010, 05:21 AM
  2. Expansion Valves
    By weighman2210 in forum Fundamentals
    Replies: 10
    Last Post: 11-02-2009, 01:49 PM
  3. Expansion Valves
    By Mukesh in forum Commercial
    Replies: 6
    Last Post: 19-09-2006, 03:11 AM
  4. Soldering Expansion Valves
    By Abe in forum Domestic
    Replies: 23
    Last Post: 18-06-2006, 01:07 AM
  5. Internal V's External Expansion Valves
    By Latte in forum Fundamentals
    Replies: 9
    Last Post: 25-06-2005, 01:12 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •