Results 1 to 17 of 17
    Scotland
    327
    Exclamation Three questions about expansion valves
    Hello
    1 - Do TEV's (internally or externally equalised) have to be fitted on a horizontal pipe or can they go on the vertical? If so, can the bulb go on the vertical?
    2 - What limits the distance between the TEV and evaporator inlet? (Without changing the design)? Would 500mm on a typical cellar cooler be ok for example?
    3 - Is it ok to use reducers either side of a TEV?
    Thanks.
    11,025
    Re: Three questions about expansion valves
    Three questions but only two numbered, you're trying to trick us
    Quote from the Sporlan documents on TEV...
    TEVs may be mounted in any position, but they should be installed
    as close to the evaporator as possible.
    Have a read up on their literature, there is a lot that can be learned from them, I know I do.
    http://www.sporlanonline.com/literature.shtml
    Scotland
    327
    thanks brian
    third quetion now added, apologies
    Oct 2003
    5,630
    34
    In most split and multisplit systems, the expansion valve is in the outdoor unit, so....
    Scotland
    327
    This is for a lu-ve cellar cooler and two lu-ve cabinet evaporators. Lu've instructions say the TEV should be directly onto the distributor and that the bulb has to be 500mm away, but I don't have room.
    11,025
    Quote Originally Posted by Contactor View Post
    There's your answer.
    May 2008
    66
    802
    Hey Peter,
    yore wright to, but this is because the are reverseble heating/cooling.....yes?
    Ice
    Mar 2005
    58
    110
    Quote Originally Posted by icecube51 View Post
    Hey Peter,
    Ice
    Also most of the 'Only Cooling' types have the expansion device (capilary or valve) in the outdour unit. Main reason : noise limitation in the indoor unit.
    Feb 2009
    bruges
    45
    42
    noise limitation in the indoor unit = true
    tip : always check the way the bulp or sensor is connected to the tube. (this could save compressor lives )
    Nov 2009
    Minsk, Belarus
    171
    15
    Danfoss says that maximum distance between TEV and evaporator ilnet would never been more than distance equal 7 diameters of connected liquid pipe.
    In some places will have to think ...
    Nov 2009
    Minsk, Belarus
    171
    15
    Yes it can be...but usually it place in horizontal pipe...
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by Aik View Post
    By evaporator inlet did you mean distributor?
    Nov 2009
    Minsk, Belarus
    171
    15
    Yes, distributor.
    Split Croatia
    57
    6,151
    36
    When you installing TXV on evaporator with distributor, place valve exit vertically (preferably downward) in order that gravity has no influence on equal distribution of liquid refrigerant.
    Scotland
    327
    Presumably Danfoss are saying that because they have to have something to design to rather than being essential. Also pointing it downwards on the vertical would be under ideal conditions.
    I suppose if you have it one metre away at an angle it will still do the job, right?
    Mar 2009
    KZN, South Africa
    64
    2,212
    If you have some distance between TXV & distributor, try to make the elbows - if any - as large radius sweeps. What most of the literature is really bleating about is trying to keep the 2-phase fluid as a mixture rather than have it separate into a liquid only & vapour only stream. This could make the distributor's life a little more tricky.
    Noise can also become a bit of an issue with long lengths plus elbows between TXV & distributor.
    Can you do it? Yes, sure - it works, as long as you are careful. If it didn't, then how on earth do the TXV's in outdoor units get the job done? How many techs bother overly with the 2-phase line between outdoor unit & indoor evap?
    ireland
    1,450
    41
    Bulbs ideally on horizontal, you can use reducers either side of the valve, can you place even a short piece of pipe vertically into the distributor? I've stuck valves externally to rooms especially where space is tight.
    alec
  1. electronic expansion valves
    By bill1983 in forum Supermarket Refrigeration
    Last Post: 23-02-2010, 05:21 AM
  2. Expansion Valves
    By weighman2210 in forum Fundamentals
    Last Post: 11-02-2009, 01:49 PM
  3. Expansion Valves
    By Mukesh in forum Commercial
    Last Post: 19-09-2006, 03:11 AM
  4. Soldering Expansion Valves
    By Abe in forum Domestic
    Last Post: 18-06-2006, 01:07 AM
  5. Internal V's External Expansion Valves
    By Latte in forum Fundamentals
    Last Post: 25-06-2005, 01:12 PM
Tags for this Thread