    Fault 052 and 055 Carrier 30GTN100--C620



    Hello,
    Carrier 30GTN100--C620 with ComfortLink Reciprocating Liquid Chillers keep having fault T052 (Circuit A, Compressor 2 Failure) and T055 (Circuit B, Compressor 1 Failure) we had the service teach from factory came and could not find any thing wrong, and the fault came couple of times in a day, vendor suggested to upgrade firmware to increase percentage voltage imbalance.

    Thanks
    Wally



  2. #2
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    22

    Re: Fault 052 and 055 Carrier 30GTN100--C620

    Quote Originally Posted by WallyHoneywell View Post
    Hello,
    Carrier 30GTN100--C620 with ComfortLink Reciprocating Liquid Chillers keep having fault T052 (Circuit A, Compressor 2 Failure) and T055 (Circuit B, Compressor 1 Failure) we had the service teach from factory came and could not find any thing wrong, and the fault came couple of times in a day, vendor suggested to upgrade firmware to increase percentage voltage imbalance.
    Thanks
    Wally
    hi wally,this alarm will occur due to the high discharge pressure,loss of charge and fault cpcs board.note the DP at peak time. Being affect the both circuit,i think due to the high discharge pressure.