Results 1 to 9 of 9
Thread: suggestion for a good controler
25-02-2010, 06:00 PM #1
hello evry body!!!
we have a screw type and a piston type air cooled trane chiller
i like to have a good documented cotrole for changing the trane cotrole
can anyone give suggestion and send pdf to my mail:
daniel.chen@012.net.il
thanks in advance daniel
25-02-2010, 09:50 PM #2
Re: suggestion for a good controler
way do you want to change the trane controller ?
26-02-2010, 11:24 AM #3
Dixell is a good starting point.
28-02-2010, 09:08 AM #4
Yes Divell is good, carell is good but why you want to replace Trane controller. It's works very good and it's made for this system. If you are sure to replace trane controller with dixell I can help you with documentation for dixell.
Can I ask you what's a trouble with trane controller?
12-03-2010, 08:48 AM #5
hi boris
sorry for no answering for long but i been out
the cxd chiller as no documentation at all
the functionality is very poor
no superheat reading
no temperture reading of suc and discharge
just water temp reading
i like to have more sofisticated controller
beside their is no much infofor trane machine at the internet and if it was
my desition i wood chnge the all machine with carier
12-03-2010, 08:54 AM #6
hi boris again
ill be glad to recieve documentation for dixel or whatever u think is good
beside that chiller we have an rtaa217
with very old controller too
it shows a01 flickering all the time
i reset all tention ireset from the controller but no use it always flickering A01 onthe display iwander if u can help
thank in advance daniel!!!
14-03-2010, 11:47 AM #7
Hello danielch, I thing the rtaa217 controller si UCM-CLD Trane adaptive control and the fault : A0 is zone temp sensor; fault : A1 is outdoor air temp sensor. Can you check resistance of sensors and the wired conection. This trane controler is good and work. I thing if it's work don't replacement. I'll send you e-mail with dixell documentation for control screw compressor, but I have a question how much are circuits, compressors, evaporaors. Is it heat pump, is it with electronic expansion valve ( I thing it isn't ) and what you want do this controler.
07-04-2010, 11:26 PM #8
If you're game, and got some DDC people in your crew, why not stick your own DDC in and you can get out whatever data you want.
I've done a couple like that. Had two chillers go down on a luxury cruise ship so they flew us out and found the Carel controllers had flamed out. I wrote up a program on a couple of Reliable DDC controllers and threw them in. Had it all running again in 24 hrs.
We are able to get whatever alarms we want, look at the staging, carry out compressor rotation the way the engineer's wanted, get pressures, temps, status's - the whole shooting match. They love it.
Did it in a theatre as well. Had a Carrier recip bust an EXV. The cost of replacing the EXV was more than if we threw in an aftermarket EXV and changed the controller. We stuck in a DDC, wrote up the software and haven't looked back.
12-07-2010, 07:49 AM #9
you can try a new controler from Renu Electronics Pvt Ltd India.
derby air con systems are they any good
By frosty74 in forum Air ConditioningReplies: 9Last Post: 07-02-2011, 11:01 AM -