McQuay centrifugal chiller data requirement!
Hello everyone! Can anybody provide some data of McQuay water cooled centrifugal chiller. I need subcooling and comp suction superheat data under different chiller capacity (30%-100%). Thanks! I appreciate your help in advance!
-
25-02-2010, 05:53 PM #2
Re: McQuay centrifugal chiller data requirement!
Hi karl, have a look here
http://www.mcquay.com/McQuay/Literature/Literature
TooshLast edited by Toosh; 25-02-2010 at 05:55 PM.
My wife used to say you never listen to a word I say at least I think that what she said
-
28-02-2010, 02:39 PM #3
Re: McQuay centrifugal chiller data requirement!
What is the exact chiller model? What working condition do you refer?
-
01-03-2010, 05:34 PM #4
-
02-03-2010, 10:13 AM #5
Re: McQuay centrifugal chiller data requirement!
Karl,
Suction superheat will vary with the chillers capacity.
We set the suction s/heat up at full load by measuring discharge s/heat. Suction s/heat should be 1degree f and this is to hard to measure in the field, so we use discharge s/heat, set to 15 degrees f + or - 1 degree. This is for 134a. Turn off the liquid injection to set up. Subcooling is typically 8 to 10 degrees f. Contact your local McQuay office with the chillers model and serial no's, they will be able to supply you with the original design data, all centrifugal design data is different, they selected for site specific design.
Regards
MQFS OZ
-
10-04-2011, 05:19 PM #6
Re: McQuay centrifugal chiller data requirement!
Hi,
Can any one provide me the Mcquay centrifugal compressor CE 100 fittings bolts tight torque value
Thank you
-
01-05-2011, 06:44 PM #7
Re: McQuay centrifugal chiller data requirement!
Hi
The Mcquay CE 100 compressor we assembled and aaplyed oil pressure at 100 psi and tryed to turn the main shaft byhand from the roter side, but it found so tight and with out oil pressure it rotate very freely.If we apply the oil pressure while it rotate there is no tight feels but minor load experianced. Please , any one can confirm that this condition is normal or not and if there is any problem, what may the cause. Your advice is very much appreciable and
thanks in advance.
-
05-05-2011, 08:55 AM #8
Re: McQuay centrifugal chiller data requirement!
Mate, do yourself and your customer a favour, call McQuay Service in Dubai for help!!!
Similar Threads
-
McQuay Centrifugal Oil pressure
By setrite in forum Trouble ShootingReplies: 10Last Post: 13-01-2011, 01:17 PM -
mcquay centrifugal chiller 063 compressor
By maico in forum Trouble ShootingReplies: 4Last Post: 22-11-2010, 06:40 PM -
Quick fix for this leak? McQuay R134A centrifugal chiller
By kaon in forum CommercialReplies: 10Last Post: 25-08-2010, 08:05 PM -
centrifugal chiller VS absorption chiller
By Masdede in forum Air ConditioningReplies: 3Last Post: 01-03-2009, 12:28 PM -
Trane CVHE 450 R11 Centrifugal Chiller
By albertjoseph in forum Air ConditioningReplies: 4Last Post: 06-10-2008, 03:23 PM