    Need advice on R-22 flooded system



    Hello All,

    I have recently "inherited" a continous ice cream freezer (Soren) with a flooded type barrel. Basically the system runs smoothly during operation. However, during start-up the condenser safety valve will blow due to high pressure at 24 bars (condenser rating is at 30 bars design pressure). FYI, the condenser water pump is switched on even when the unit is in shutdown.

    On operation side, during flavour change (prior to start-up), hot water is allowed to flow through the barrel (flooded evaporator) for CIP (clean in place). Could this cause the liquid to evaporate and create a pressure build up at the condenser?

    Will pumping down the system prior to CIP completely eliminate the problem or are there other recommended modifications to the system. Previous experience in pumping down the system causes oil to accumulate at the condenser.

    Thanks in advance for any advice/help/suggestions.

    PS: Normally we relieve the gas, start up the system, and recharge the system again which I find quite baffling .



  2. #2
    Join Date
    May 2009
    Location
    Sydney
    Posts
    73
    Rep Power
    15

    Re: Need advice on R-22 flooded system

    Do you have a crankcase pressure regullator fitted to the system?

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Need advice on R-22 flooded system

    You did not mention what is the pressure after you charge the system.
    Is it one compressor or a few?
    You need an oil separator if you loose oil.

    Pump down is vital if you wash the barrel with hot water. There is liquid refrigerant insideand the pressure is too high.

    Its the same method in DX milk tanks, always pump down before washing with hot water [ 80°C]

  4. #4
    Join Date
    Sep 2009
    Location
    Malaysia
    Posts
    6
    Rep Power
    0

    Re: Need advice on R-22 flooded system

    The system is charged to:

    Discharge pressure: 240 psig
    Suction pressure: 0 psig

    According to the user manual, 50 kgs of R-22 is required.

    A back pressure regulator is installed right after the cooling barrel, before the suction accumulator.

    We have recently replaced the old oil seperator with one size up and solved the low oil pressure problem. However, yesterday we had a safety valve blow out again and we had been running at 200 psig discharge and 0 psig suction. However, this causes the compressor to frequently trip on low oil pressure.

  5. #5
    Join Date
    Sep 2009
    Location
    Malaysia
    Posts
    6
    Rep Power
    0

    Re: Need advice on R-22 flooded system

    Forgot to mention that this is a single compressor system (Bitzer S6H 20.2 compressor).

  6. #6
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Need advice on R-22 flooded system

    .

    You need to think about what could cause this,
    I know you already have but I mean at a very basic level.

    What is different now to when it was ok?

    What would cause the discharge pressure to high on start
    up when it is not on normal running.

    The first thing that comes to mind is back pressure
    (suction pressure). The suction pressure is too high
    initially untill the comp gets hold of the pressures??

    Or could there be air in the system. If the back pressure
    is 0 then it could have pulled air in and maybe that is a problem..

    all the best

    taz

    .

  7. #7
    Join Date
    Sep 2009
    Location
    Malaysia
    Posts
    6
    Rep Power
    0

    Re: Need advice on R-22 flooded system

    Thanks for the advice Taz. Perhaps I HAD overlooked the most basic of refrigeration (leak test) since we've been discharging and recharging so often, it is not obvious if we have a leak problem.

    Will keep you guys updated once I can arrange for proper leak test.

  8. #8
    Join Date
    Sep 2009
    Location
    Malaysia
    Posts
    6
    Rep Power
    0

    Re: Need advice on R-22 flooded system

    Hello again everyone, just an update, completed leak testing and re-modifying the system. Following are what went wrong:

    1) System was previously modified so as the system's receiver tank inlet to be located AFTER the solenoid valve, effectively disabling it during pump down (thus causing the condenser to blow its safety valve). This have been rectified.

    2) The receiver tank was "blamed" for the slow startup after CIP. It has been found that the inlet and outlet of the receiver tanks were swapped around (liquid in connected to bottom of the tank while outlet was on top of the tank) during previous modifications. This was rectified as well.

    Currently putting the system to test after modification works.

    Thanks for everyone's help so far.

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Need advice on R-22 flooded system

    The compressos are loading too fast. Slow and easy is recommended. Hence why system operates OK at design, but not during pulldown. Tell the production ****heads to wait until system has stabilized and ready to operate.
    magoo

  10. #10
    Join Date
    Sep 2009
    Location
    Malaysia
    Posts
    6
    Rep Power
    0

    Re: Need advice on R-22 flooded system

    Thank all for the help offered so far. After modifying, the system (Figure 2 as per attached) is running stable for 5 days so far .

    However, prior to modifying, we also considered to go for an alternate arrangement (Figure 1: Proposed System as per attached). The reason is that the system as per proposed in Figure 1 would keep all the liquid in the receiver tank and then from the receiver goes to the intercooler/expansion valve.

    Which would be the proper configuration?

    Thanks in advance.

    Figure01.jpg
    Figure02.jpg

Similar Threads

  1. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  2. Thermobank system from Kramer
    By ardi in forum New Technologies
    Replies: 7
    Last Post: 14-06-2007, 01:00 PM
  3. Flooded R22 system
    By Steve Wright in forum Fundamentals
    Replies: 17
    Last Post: 06-02-2006, 09:14 AM
  4. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •