    How to calculate volume flow of the pump for
    R-507 for flooded evaporator W=400kW, -40 C
    3,356
    Re: Pump for flooded evaporator
    Calculate amount of refrigerant flow through compressor and usually multiply by 4 for a 4 to 1 curculation ratio .
    ie ciculate 4 kg refrigerant and only 1 kg turns to gas as a rough rule .
    You may have to find out evaporator design circulation rate .
    If its only 1 evaporator you may have a problem as pumps of this style could be way to big if small evaporator
    Aug 2008
    California
    28
    The long answer…
    Find the R-507 thermodynamic tables
    Look up suction vapor enthalpy value
    Look up the liquid feed enthalpy valve
    Subtract the liquid enthalpy from the vapor enthalpy
    This is your refrigeration effect
    Divide your desired load (400kw) by the refrigeration effect
    This is your mass flow rate
    Divide your mass flow rate by your liquid density
    This is your raw volumetric flow rate
    Multiply your raw volumetric flow rate by the recirculation rate (say 4 for flooded)
    This is the amount you need to pump.
    Apr 2009
    Israel
    63
    5
    How much Pump Circulation Rate
    should be ?
    Nov 2004
    China
    176
    Circulation rate is a function of the circuit design within the evaporator. I've seen as low as 1.1 to 1 and as high as 5 to 1. 3 to 1 and 4 to 1 are most common for air cooling evaporators.
    Apr 2009
    Israel
    63
    5
    Quote Originally Posted by charlie n View Post
    Thanks, but what is better for shock freezing -40C?
    Nov 2004
    China
    176
    Probably 4:1 is the most common recirculation rate. Ask your evaporator coil manufacturer. For example, one of the Canadian manufacturers makes down fed aluminum evaporators using 5:1 so it really depends on the evaporator design.
    Aug 2008
    California
    28
    Remember R-507 is expensive, going 4-1 means you need to have a larger pipe to reduce the friction losses though the pipe. Also you will have a larger refrigerant charge. Your evaporator efficiency will go up with 4-1 but so will your costs. consider economizing on the liquid feed to say 2-1 or 3-1. This may save you money in the long run.
    Nov 2004
    China
    176
    Better still, build the freezer for ammonia.
    Auckland
    74
    3,357
    37
    Hi Decosta.
    very good explantion of what happens and what is required.
    magoo
    Apr 2009
    Israel
    63
    5
    Unfortunately there is no permission
    Nov 2004
    China
    176
    I remember being told that about a skating rink installation in your country but I had hoped the authorities would have seen the light in the case of an industrial situation. Unfortunately not.
  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Last Post: 15-01-2011, 01:24 AM
  2. EVAPORATOR leaked
    By James priyono in forum Air Conditioning
    Last Post: 23-05-2009, 10:19 AM
  3. Replies: 14
    Last Post: 27-08-2008, 08:57 PM
  4. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  5. Evaporator Design-Air Source Heat Pump for water heating
    By anup in forum Technical Discussions
    Last Post: 20-03-2006, 02:26 PM