Thread: desuperheater issue
22-02-2010, 07:55 AM #1
desuperheater issue
Hi sirs
As I know ,the desuperheater is used to removing the discharge superheat. If the desuperheater oversized, how about the affect on the series condenser ? I think the desureheater can bring two-phase refirirant flow to the condenser and cause distribution problem or others.
Hope your comments. thanks!
with Chinese Tiger year best wishes
LC
22-02-2010, 08:56 AM #2
Re: desuperheater issue
Hi LC,
Have you done any experimental tests on the de-superheater / condenser series configuration?
What did your results show?Engineering Specialist - Cuprobraze, Nocolok, CD Technology
27-02-2010, 08:14 PM #3
You are right about the 2-phase flow.
As to distribution at the condenser: You can certainly cause issues though distribution would probably not be the first.
The management of charge and its availability to the evaporator is usually the first thing to go fuzzy when you add heat rejection on the high side.
But operating at low discharge pressures often causes lubrication issues too..Though not fro the same reasons as the refrigerant charge issues.
Read up on Head Pressure control from the Control Valve folks; and then Heat Recalim from the same...Also Oil Return and Oil Separator from those who make small vessels.
05-03-2010, 08:20 AM #4
I see your point. To keep a proper head pressure is the important isue.
Daikin output overcurrent issue
By wilson77 in forum Air ConditioningReplies: 15Last Post: 18-01-2010, 11:36 PM -
Beko Fridge freezer - freezer temp issue
By lukas989 in forum DomesticReplies: 2Last Post: 30-09-2009, 05:29 PM -
Trane Weathertron 900 XE wierd issue
By trader_Mike in forum Trouble ShootingReplies: 5Last Post: 11-08-2009, 11:08 PM -
Flood back issue?
By Arc in forum Trouble ShootingReplies: 15Last Post: 28-10-2008, 03:40 PM -
hydraulic floor heating issue
By Lc_shi in forum New TechnologiesReplies: 6Last Post: 02-01-2007, 09:07 PM