Results 1 to 3 of 3
  1. #1
    Join Date
    Aug 2008
    Location
    glasgow
    Posts
    20
    Rep Power
    0

    Exclamation samsung error code



    in need of help, i have a samsung split system uh060eav inverter 410a, hard wired controler. intermitently fault code 458 comes up unit shuts down. ambiant temp has been -6 recently. any feed back i would be greatfull of.



  2. #2
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    19

    Re: samsung error code

    please see below:

    458 outdoor fan error

    Check the input power connection status
    • Check the connection status between the motor
    and PCB in outdoor unit
    • Check the fuse of indoor/outdoor units
    Paul


    "KEEP IT COOL"

  3. #3
    Join Date
    Aug 2008
    Location
    glasgow
    Posts
    20
    Rep Power
    0

    Re: samsung error code

    thanks for your help, will attend sight tomorrow