    working with a hitachi utopia ac split indoor rpk 4aq5
    suspect blockage after leaving condensing unit. ( me thinks its in the indoor)

    what i want to know is what kind off expansion is used in this system and has anyone any tips were to check for a blockage?

    cannot remove indoor fascia as some numpty has ran cable tray right along the front of the unit
    (still plenty of airflow tho)
    Last edited by chillin out; 19-02-2010 at 10:00 PM.



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,876
    Rep Power
    28

    Re: Hitachi

    I had a blockage a while back on a mitsi electric split.

    From memory the unit used to work on cooling but wouldn't work on heating.

    Finally traced the problem to a piece of armourflex that must have gone inside the gas pipe when they were pulling it over the copper on installation.

    The way we ended up finding it was disconnect the gas and liquid line going into the indoor and outdoor units and blow through with OFN.

    Also then u could blow through the indoor unit to see if it is this that is blocked but most indoors especially cassette types normally have gauze to stop foreign objects going inside the units.

    Also had it on another site and we had to seperate the pipework into sections and blow though, we found a 1/4 liquid line was 90% braized inside causing a massive restiction.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    240
    Rep Power
    19

    Re: Hitachi

    this is a high wall unit i put a trace down and didnt get much back thats why im thinkin indoor

  4. #4
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Hitachi

    The Utopia indoor units are compatable with VRF Set Free so have electronic expansion valve at the indoor unit.
    Make sure its plugged in at the circuit board.
    If you have service manual you can display the indoor unit electronic expansion valve opening possition on the outdoor unit circuit board display, but remember this is the command from the indoor circuit board not the actual opening possition of the valve.

  5. #5
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    240
    Rep Power
    19

    Re: Hitachi

    thanks therma , no manual tho.

  6. #6
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,471
    Rep Power
    41

    Re: Hitachi

    register with hitachi at: http://www.hitachiaircon.co.uk/argws/

    good selection of tech manauls here.

    alec

  7. #7
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    240
    Rep Power
    19

    Re: Hitachi

    thanks al i new giving u that lift would pay off one day

  8. #8
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    240
    Rep Power
    19

    Re: Hitachi

    blew it all through and got alot off oil back. no valve inside just capilary.
    now working ok

Similar Threads

  1. Hitachi "31" fault
    By ronaldo9 in forum Trouble Shooting
    Replies: 1
    Last Post: 22-02-2010, 08:26 PM
  2. Hitachi split timer LED 10 flash
    By paul_h in forum Air Conditioning
    Replies: 5
    Last Post: 12-02-2009, 01:32 PM
  3. Well Done / Thanks Hitachi UK
    By Latte in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 24-11-2008, 08:52 PM
  4. Need help on HITACHI VRF RAS10FSG-38
    By cool#9 in forum Air Conditioning
    Replies: 1
    Last Post: 21-05-2008, 01:16 AM
  5. Hitachi Inverter Systems
    By Vishnukurup in forum Air Conditioning
    Replies: 13
    Last Post: 15-11-2007, 02:15 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •