Thread: Testo 560, apparently fault
21-02-2010, 01:55 PM #1
In pdf you will find pressure/temperature scale of water and besides of this table, 3 pictures of the Testo560, 2 in Pa and 1 in Microns.
You will see that the figures on the screen of the Testo 560 doesn't match with those in the Coolpack table.
How it comes? I can't find what's wrong.Last edited by Peter_1; 21-02-2010 at 01:57 PM.
21-02-2010, 04:11 PM #2
Re: Testo 560, apparently fault
I think you are confusing the vapour pressure with the saturated evaporating pressure.
The triple point of water is 0°C, so vapor equlibrium only exists above 0°C.
21-02-2010, 04:51 PM #3
The Testo is in vacuum mode and you can see in the right corner H2O
22-02-2010, 12:31 PM #4
Resolution of instrument is 80microns and accuracy is +/-0.5% of scale. I don't think it can do any better than that. Try zeroing the instrument.
22-02-2010, 03:56 PM #5
22-02-2010, 05:25 PM #6
Coolpack can't be wrong. It's a mathematical software. I cross confirmed the output values with another software.
22-02-2010, 05:37 PM #7
NoNickname, Gerrit has a point I think, even with the given inaccuracy, the conversion between pressure and temperature must match anyhow because the Testo measures pressure and then converts it via the software to a temperature.
30-09-2011, 03:29 AM #8
I bet it has to do with the sea level adjustment in the testo. Its adjustable to where you reside.
30-09-2011, 06:14 AM #9
It starts from zero and the adjustment was done. Still not solved.
30-09-2011, 06:16 AM #10
30-09-2011, 07:41 AM #11
Hey Peter_1, and Figaro
This is my Testo560, and he is set to sea level
Until now no reply received from Testo
Still in limbo
I meet them soon on exhibitions
Hitachi "31" fault
By ronaldo9 in forum Trouble ShootingReplies: 1Last Post: 22-02-2010, 08:26 PM -
Daikin r407c 2 pipe vrv ja fault code any offers?
By Contactor in forum Air ConditioningReplies: 11Last Post: 28-07-2009, 01:26 AM -
Fault with Tango cassette
By airefresco in forum Air ConditioningReplies: 8Last Post: 19-09-2007, 08:42 AM -
UA Daikin Fault Code
By jedi in forum Air ConditioningReplies: 2Last Post: 23-07-2007, 01:44 PM -
Chiller fault
By iceman007 in forum Trouble ShootingReplies: 9Last Post: 27-06-2006, 06:15 AM
