19-02-2010, 05:40 PM #1
working with a hitachi utopia ac split indoor rpk 4aq5
suspect blockage after leaving condensing unit. ( me thinks its in the indoor)
what i want to know is what kind off expansion is used in this system and has anyone any tips were to check for a blockage?
cannot remove indoor fascia as some numpty has ran cable tray right along the front of the unit
(still plenty of airflow tho)Last edited by chillin out; 19-02-2010 at 09:00 PM.
-
19-02-2010, 06:59 PM #2
Re: Hitachi
I had a blockage a while back on a mitsi electric split.
From memory the unit used to work on cooling but wouldn't work on heating.
Finally traced the problem to a piece of armourflex that must have gone inside the gas pipe when they were pulling it over the copper on installation.
The way we ended up finding it was disconnect the gas and liquid line going into the indoor and outdoor units and blow through with OFN.
Also then u could blow through the indoor unit to see if it is this that is blocked but most indoors especially cassette types normally have gauze to stop foreign objects going inside the units.
Also had it on another site and we had to seperate the pipework into sections and blow though, we found a 1/4 liquid line was 90% braized inside causing a massive restiction.The difference between genius and stupidity is that genius has its limits.
Marc
-
19-02-2010, 07:39 PM #3
Re: Hitachi
this is a high wall unit i put a trace down and didnt get much back thats why im thinkin indoor
-
19-02-2010, 08:39 PM #4
Re: Hitachi
The Utopia indoor units are compatable with VRF Set Free so have electronic expansion valve at the indoor unit.
Make sure its plugged in at the circuit board.
If you have service manual you can display the indoor unit electronic expansion valve opening possition on the outdoor unit circuit board display, but remember this is the command from the indoor circuit board not the actual opening possition of the valve.
-
19-02-2010, 08:47 PM #5
Re: Hitachi
thanks therma , no manual tho.
-
19-02-2010, 09:00 PM #6
Re: Hitachi
register with hitachi at: http://www.hitachiaircon.co.uk/argws/
good selection of tech manauls here.
alec
-
19-02-2010, 09:34 PM #7
Re: Hitachi
thanks al i new giving u that lift would pay off one day
-
22-02-2010, 08:55 PM #8
Re: Hitachi
blew it all through and got alot off oil back. no valve inside just capilary.
now working ok
Similar Threads
-
Hitachi "31" fault
By ronaldo9 in forum Trouble ShootingReplies: 1Last Post: 22-02-2010, 07:26 PM -
Hitachi split timer LED 10 flash
By paul_h in forum Air ConditioningReplies: 5Last Post: 12-02-2009, 12:32 PM -
Well Done / Thanks Hitachi UK
By Latte in forum Chit Chat & Service StoriesReplies: 4Last Post: 24-11-2008, 07:52 PM -
Need help on HITACHI VRF RAS10FSG-38
By cool#9 in forum Air ConditioningReplies: 1Last Post: 21-05-2008, 01:16 AM -
Hitachi Inverter Systems
By Vishnukurup in forum Air ConditioningReplies: 13Last Post: 15-11-2007, 01:15 PM