    siemens expansion valve



    Yello

    after all the conclusions i believe the expansion valve is defective , and i wouldn't want to replace it for nothing, my question is how much experience do you have with siemens electronic expansion valves, because in the chiller that is with problems, there are 2 (out of 4) that have the same symptom and it's my firs expansion valve of this size that i see in trouble.

    so ... did anybody had problems with siemens electronic expansion valves

    For the data's to be complete , model MVL661.25-6.3



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: siemens expansion valve

    Why dont you explain symptoms?

  3. #3
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: siemens expansion valve

    i have a large pressure loss across the valve , from 15 bar before to 1 bar after when the screw is at 100% and the valve is fully open , and condenser water 20 deg C, and evaporator water at 10 deg C, and it is going to low pressure alarm because the pressure after the valve never rises above 2 bar (refrigerant R407).

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: siemens expansion valve

    I have very good experience with polycool valves from Siemens, and never found any one faulty, so far. Not even after many years.
    Your symptom is typical of a wrongly set dip switch in the valve box. There is one dip switch which limits the max throughput to 63% of the valve max flow rate. Check that one, before assuming the valve is faulty.
    Also, did you go through the whole list of parameters? Are they consistent across the four valves?

  5. #5
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: siemens expansion valve

    yes the 63% limit is active, but so it is on the one of the circuit that is running ok, so i didn't gave more attention to the switches.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: siemens expansion valve

    Well, you may try to put it to 100% and see whether this makes a difference. If not, than really some sort of clogging is present.

  7. #7
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: siemens expansion valve

    i could but i'm shore that there is less then 2% probability that it is going to work

Similar Threads

  1. hunting expansion valve on airedale c/control
    By knight rider in forum Technical Discussions
    Replies: 28
    Last Post: 10-07-2009, 11:21 PM
  2. Actual Expansion Valve Process
    By AastroGuru in forum Fundamentals
    Replies: 11
    Last Post: 03-02-2009, 10:53 AM
  3. Setting of Hand expansion valve
    By Iceehot in forum NH3
    Replies: 7
    Last Post: 10-09-2008, 01:25 AM
  4. the function of the electronic expansion valve
    By Crystal-426 in forum Fundamentals
    Replies: 10
    Last Post: 22-06-2008, 12:29 PM
  5. Need Divine Intervention - plugged drier or expansion valve?
    By archibaldtuttle in forum Trouble Shooting
    Replies: 4
    Last Post: 08-06-2008, 06:52 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •