    How to measure air flow



    Hi Everyone,

    I was wondering what exact method you guys use to determine CFM on wall mount Indoor units? I assume its somewhat different from a ducted unit. Would you simply use manufacture air flow specs for the unit you are working on.


    Thanks in advance.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: How to measure air flow

    Yup.

    If you need to check on units on a regular basis I would take a velocity reading on a new unit and record it. Compare the reading at later visits to indicate potential faults.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2008
    Location
    USA
    Age
    52
    Posts
    98
    Rep Power
    17

    Re: How to measure air flow

    Quote Originally Posted by Brian_UK View Post
    Yup.

    If you need to check on units on a regular basis I would take a velocity reading on a new unit and record it. Compare the reading at later visits to indicate potential faults.
    Thank you!

  4. #4
    Join Date
    Apr 2009
    Location
    WI USA
    Posts
    27
    Rep Power
    0

    Re: How to measure air flow

    Quote Originally Posted by Husky250 View Post
    Hi Everyone,

    I was wondering what exact method you guys use to determine CFM on wall mount Indoor units? I assume its somewhat different from a ducted unit. Would you simply use manufacture air flow specs for the unit you are working on. Thanks in advance.
    Use a good anemometer & the formula: supply face velocity in FPM *X's area in sq.ft. = CFM

    If the supply outlet measurements are given, or you can measure it, divide the sq.ins., by 144 to get sq.ft., then multiple by the average cross-section airflow velocity in feet per minute (FPM) to get CFM.

    Compare the resulting CFM to the mfg'ers listed rating(s).

    That works the same way on duct supply diffusers. That can provide a ball-park CFM, perfect precision is near impossible when measuring airflow. You're trying to see if it is too far off where airflow should be.

    To find open area of a round duct; Duct diam is 7"; 7"X7"= 49 X's .7854 = 38.04845-sq.ins divided/ by 144= 0.2672541-sq.ft. area X's FPM Velocity 600-FPM = 160-CFM.

    Especially in the cooling mode; Correct Airflow is extremely important to operating performance & efficiency.
    Last edited by udarrell; 22-02-2010 at 04:51 PM. Reason: clarifications...

Similar Threads

  1. flow switch connection
    By afeef in forum The Trail of Tears
    Replies: 18
    Last Post: 23-12-2009, 07:55 PM
  2. Pulling faster vacuums
    By Aranon in forum Fundamentals
    Replies: 31
    Last Post: 04-09-2009, 07:32 PM
  3. Flow Rate through Fan Coil Unit
    By deepu in forum Air Conditioning
    Replies: 4
    Last Post: 21-07-2009, 06:42 AM
  4. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 02:03 PM
  5. Refrigerant flow rates/gas laws
    By budro in forum Technical Speculations
    Replies: 3
    Last Post: 24-10-2008, 03:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •