    Defrost Problem Carrier 38ARQ



    When the unit goes into defrost there are issues happening.

    1. The Y circuit cuts out. Compressor goes off.
    2. The Outdoor Fan goes off like normal.
    3. The Defrost board has an internal relay that has two normally open switches. One for EH and the other for RVS. This relay just starts clicking.
    4. It will continue indefinately or until you turn off power and turn back on.
    The unit will run fine in Heat Mode or Cool and if you jump R directly to RVS while in Heat Mode it will switch and no problems with losing the Y.

    Things we have done.

    1. We have replaced the Defrost Board thinking it was bad.
    2. The problem was still present. We troubleshooted and decided to try changing the board again thinking maybe we got a bad one.
    3. Same thing continued.

    Any Idea's?

    Wrangoth



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Defrost Problem Carrier 38ARQ

    Loose connections, poor neutral ?

    Check circuit for continuity.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2010
    Location
    USA
    Age
    56
    Posts
    8
    Rep Power
    0

    Unhappy Re: Defrost Problem Carrier 38ARQ

    There is a relay in the air handler that energizes through the call for RSV. The Y circuit is on a normally open switch and when the relay would energize to open outdoor dampers the problem would occur.

    It only would happen when the unit tried to go into defrost. When the unit was in cool it would run fine. Kinda confusing.

    We took the Y circuit off the relay and bypassed the relay and outside dampers. Problem went away. So, we the unit is workingj and will go into defrost but the outside air dampers are not working. Will be looking further..... later.

    Thanks

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. maytag fridge activation of new controller
    By jdrefrigeration in forum Domestic
    Replies: 5
    Last Post: 09-03-2010, 12:00 PM
  3. Problem with Carrier 511-331
    By ci_1612 in forum Transport
    Replies: 1
    Last Post: 03-01-2010, 08:13 AM
  4. Toshiba RAV SM/SP1400 defrost problem
    By SteinarN in forum Heat Pumps
    Replies: 11
    Last Post: 20-02-2008, 04:25 PM
  5. No Power for Defrost Timer Motor
    By kln in forum Domestic
    Replies: 6
    Last Post: 21-01-2008, 08:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •