16-02-2010, 11:41 PM #1
Frick rwb ii coalescers
I just changed my first coalescers last week. Not as bad as I was told it would be. Just had a heck of a time trying to get the manway gasket to line up all the way around the manway cover. I used a little bit of tape to hold it on while I tightened it up. Is there a easier way to do this like use a adhesive to hold the gasket in place?
-
17-02-2010, 01:48 AM #2
Re: Frick rwb ii coalescers
Using a contact adhesive works well for me. This is recommended by FES on their machines.
To continue a bit, I like to make my own out of Neoprene when possible. 50-60 Durometer works well. For ***** machines virgin Neoprene is recommended.
I like 1/8" material. Thicker is not better. A thick gasket can, and will blow out.
Another note: before you start to depressurize a compressor to change the coalescer, always tighten the manway cover. If you do not it may start to leak as the pressure drops.
(I learned these things the hard way)
-
17-02-2010, 05:17 PM #3
Re: Frick rwb ii coalescers
NH3s On a similar note, I use STP for holding O rings in place when changing disposable oil filters. C.D.
NH3 for me
-
18-02-2010, 01:36 AM #4
Re: Frick rwb ii coalescers
Yeah, some guys showed me they like nickel plate anti seize, or armite led plate 250
Similar Threads
-
problem with volume on frick screw compressor
By samlee12 in forum IndustrialReplies: 4Last Post: 29-10-2009, 06:06 AM -
Big Frick was locked up
By bruceboldy in forum Industrial CompressorsReplies: 8Last Post: 08-08-2009, 03:45 PM -
problem with frick screw volume
By samlee12 in forum Industrial CompressorsReplies: 9Last Post: 20-06-2009, 02:46 PM -
Frick compressor RXF 101-H
By PaulZ in forum Industrial CompressorsReplies: 11Last Post: 19-02-2009, 02:29 AM -
Ammonia Circulation rate - by Frick/ Vitler
By smpsmp45 in forum NH3Replies: 12Last Post: 16-06-2008, 10:06 AM