Thread: condensing unit sizing
-
16-02-2010, 10:16 PM #1
condensing unit sizing
if i have a existing evaporator and the condensing unit is knackered how would i go about selecting a new condensing unit?
-
16-02-2010, 10:23 PM #2
Re: condensing unit sizing
Get one that is the same duty.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
16-02-2010, 11:15 PM #3
Re: condensing unit sizing
it a 1.5hp / 1.1kw is this enough to match with?
-
17-02-2010, 01:00 PM #4
Re: condensing unit sizing
If you can list more information such as; application, refrigerant, temp, any model numbers you have etc. We might be able to help.
Thousands of HVACR manufacturers links! Visit: www.hvacrinfo.com
-
20-02-2010, 09:22 PM #5
Re: condensing unit sizing
Measure the old one.
Measure the pipes and length and measure the height...
There you are you have the same ...
-
23-02-2010, 04:08 AM #6
-
28-02-2010, 04:24 PM #7
Re: condensing unit sizing
Talk to your local wholesaler with a model and serial of the condensing unit or specifications on your system. They will be able to find you exactly what you are looking for
-
28-02-2010, 05:36 PM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
28-02-2010, 10:33 PM #9
Re: condensing unit sizing
match the unit to the evaporator capacity(kw or btu etc) at what designed suction temperature,refrigerant and condensing ambient temperature,this will put you in the ball park
mmm to beer or not to beer...........lets drink breakfast
Similar Threads
-
DX capacity lower than condensing unit
By M.Saleh in forum Air ConditioningReplies: 2Last Post: 18-01-2010, 03:01 AM -
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 07:23 PM -
M I T S U S H I T A ac unit with no condensing unit
By Chinua in forum Air ConditioningReplies: 2Last Post: 28-07-2006, 06:54 PM -
Matching Evaporator with Condensing Unit
By Abe in forum Technical DiscussionsReplies: 12Last Post: 25-07-2001, 08:57 AM