    Mar 2008
    52
    98
    How to measure air flow
    Hi Everyone,
    I was wondering what exact method you guys use to determine CFM on wall mount Indoor units? I assume its somewhat different from a ducted unit. Would you simply use manufacture air flow specs for the unit you are working on.
    Thanks in advance.
    11,025
    Re: How to measure air flow
    Yup.
    If you need to check on units on a regular basis I would take a velocity reading on a new unit and record it. Compare the reading at later visits to indicate potential faults.
    Mar 2008
    52
    98
    Yup.
    Thank you!
    Apr 2009
    WI USA
    27
    Quote Originally Posted by Husky250 View Post
    Hi Everyone,
    I was wondering what exact method you guys use to determine CFM on wall mount Indoor units? I assume its somewhat different from a ducted unit. Would you simply use manufacture air flow specs for the unit you are working on. Thanks in advance.
    Use a good anemometer & the formula: supply face velocity in FPM *X's area in sq.ft. = CFM
    If the supply outlet measurements are given, or you can measure it, divide the sq.ins., by 144 to get sq.ft., then multiple by the average cross-section airflow velocity in feet per minute (FPM) to get CFM.
    Compare the resulting CFM to the mfg'ers listed rating(s).
    That works the same way on duct supply diffusers. That can provide a ball-park CFM, perfect precision is near impossible when measuring airflow. You're trying to see if it is too far off where airflow should be.
    To find open area of a round duct; Duct diam is 7"; 7"X7"= 49 X's .7854 = 38.04845-sq.ins divided/ by 144= 0.2672541-sq.ft. area X's FPM Velocity 600-FPM = 160-CFM.
    Especially in the cooling mode; Correct Airflow is extremely important to operating performance & efficiency.
  1. flow switch connection
    By afeef in forum The Trail of Tears
    Last Post: 23-12-2009, 06:55 PM
  2. Pulling faster vacuums
    By Aranon in forum Fundamentals
    Last Post: 04-09-2009, 07:32 PM
  3. Flow Rate through Fan Coil Unit
    By deepu in forum Air Conditioning
    Last Post: 21-07-2009, 06:42 AM
  4. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Last Post: 10-03-2009, 01:03 PM
  5. Refrigerant flow rates/gas laws
    By budro in forum Technical Speculations
    Last Post: 24-10-2008, 03:12 AM