Daikin U4 fault, power down and reboot sequence
What is the procedure for powering down then powering up a daikin vrv system
Also how long does the boot up sequence take?
-
15-02-2010, 07:42 PM #2
Re: Daikin U4 fault, power down and reboot sequence
Hi,
What is the unit model number? If the unit is K, L, M or P series, switch off indoors at controllers then switch off mains power.
Switch on mains power and wait for H2P LED on the outdoor unit pcb to change from flashing (initialising) to off, usually takes about 10~15min.
-
16-02-2010, 06:50 PM #3
-
16-02-2010, 08:10 PM #4
Re: Daikin U4 fault, power down and reboot sequence
Hi,
When switching off - It makes no difference but switch off at controllers first.
When applying power - Indoors & BS boxes first then outdoor. However it wouldn't make any difference providing you switch outdoor mains off/on when you have power to all connected indoors (& BS boxes if heat recovery).