    Zenith Dehumidifier



    I have a year old Zenith Dehumidifier that quit Dehumidifying. The compressor ran but no delta T on the pipes. The service port looked like it was crimped and braised by a chimp and I am sure that is were the leak was. I cut the stub off (high side) and installed a schreder fitting. The pressure was just above ambient when I cut into it. Not knowing how much ***** to put in (R-22) I put in about 3 OZ. The compressor would start but the current draw was high and no delta T to speak of and the inlet pipe from the filter to the compressor started to ice up. Turning the unit off and then back on relieved a stalled compressor. I took about 1/2 oz of ***** out and the unit started working. but still stalls unless the off time is a bit over 5 min. the performance seems a bit low. what is a good way to find the sweet spot on the amount of ***** for this unit?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Zenith Dehumidifier

    Charge by sub-cooling.

    Did you do a leak test before you recharged it? Leak may have sucked in air and moisture could be blocking the pinch points.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2009
    Location
    Florida
    Posts
    15
    Rep Power
    0

    Re: Zenith Dehumidifier

    As I mentioned it had positive (slight) pressure in it. I leak checked it after I fitted the service valve I purged it with dry nitrogen and pulled a hard vacuum which it held over night. It is now working but I think it is over serviced. I will check the sub cool as you suggest.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Zenith Dehumidifier

    I appreciate the positive pressure but I was thinking about the unit running and possibly pulling a vacuum due to the low charge. You seem to have covered that problem anyway.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Dec 2009
    Location
    Florida
    Posts
    15
    Rep Power
    0

    Re: Zenith Dehumidifier

    I pulled some ***** out until I got about 6 Deg SC and the unit seems to be working correctly. Thanks for the advice.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Zenith Dehumidifier

    OK, thanks for the update.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. dehumidifier problems
    By kfox@miindustri in forum Fundamentals
    Replies: 2
    Last Post: 19-11-2008, 07:26 PM
  2. liquid fresh air dehumidifier
    By Lc_shi in forum New Technologies
    Replies: 0
    Last Post: 17-10-2008, 07:48 AM
  3. Superheat on a dehumidifier?
    By Larry2 in forum Domestic
    Replies: 0
    Last Post: 10-08-2007, 10:57 PM
  4. LG Dehumidifier
    By Larry2 in forum Trouble Shooting
    Replies: 5
    Last Post: 21-09-2006, 05:55 AM
  5. household portable dehumidifier
    By Lc_shi in forum Fundamentals
    Replies: 15
    Last Post: 29-08-2005, 10:30 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •