    Dual temperature refrigeration



    Is there such a patented refrigation system which can operate a storage room either as a cold room (+5 deg C) or as a freezer (-18 deg C) at the touch of a button. I can think of different ways of organising a refrigeration system to do this, but can one buy a system already designed for that purpose ?

    Harry



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Dual temperature refrigeration

    Harry who,
    money can do anything so long as you are prepared to spend.
    Did a couple for the AirForce here, worked sweet as, expensive though.
    Don't now about patents, as is regular refrigeration design, sorry bud. Check out regular transport refrig., systems and similar. Flick a switch between fresh or frozen.
    magoo

  3. #3
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Dual temperature refrigeration

    Yes there are systems ready to use type made by Zanotti/ Technoblock etc & we have used them as well.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Dual temperature refrigeration

    If you are concerned about patents then you should check with the Patent Office also.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Dec 2009
    Location
    usa
    Posts
    6
    Rep Power
    0

    Re: Dual temperature refrigeration

    Fairly common in supermarkets using "dual temp" cases. The switch energizes a bypass solenoid around an EPR and allows the case to run at compressor suction pressure (low temp). Release the bypass and the EPR will modulate and hold the pressure up in the evaporator and increase its SST.

  6. #6
    mefleh's Avatar
    mefleh Guest

    Re: Dual temperature refrigeration

    i guess there no problem of opert condensing unit for both +5 or -18 c as far there is heater inside the evaporatore and time for defrost should be evry 6 working hours

Similar Threads

  1. advanced refrigeration technology
    By Lc_shi in forum Fundamentals
    Replies: 10
    Last Post: 16-02-2011, 06:22 PM
  2. LG heat pump problem
    By back2space in forum Heat Pumps
    Replies: 132
    Last Post: 02-02-2009, 12:23 AM
  3. Wrong temperature on control panel
    By swee'pea in forum Trouble Shooting
    Replies: 2
    Last Post: 14-01-2009, 10:18 AM
  4. Carbon Dioxide Refrigeration
    By Andy in forum CO2
    Replies: 101
    Last Post: 12-08-2008, 03:33 AM
  5. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •