    outdoor fan not starting



    Hi Guys,
    I'm from Bulgaria and probably a "tiny" fault has been pestering me for long time.

    I have a Midea 12000 BTU,R22, on-off split air conditioner. It has only one temperature-pressure pipe sensor on the indoor coil which controls the outdoor fan operation and defrost. In heat mode when you start the air conditioner initially the outdoor fan motor starts but in a minute it stops and never comes back on, expect for when there is a thick layer of ice on the outdoor coil. When I take out the indoor coil thermister the fan stays on, but defrost is not working.
    Without the outdoor fan running the system doesn't give enough heat, when the thermister is of the tube ice build up after a while (24 hours).
    The problem is definitely not the charge as I have recharged the unit with new refrigerant by weight!
    Pipe run is 3.5 meters.
    What can be the reason for this nasty fault?Restriction in the system?



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: outdoor fan not starting

    Faulty controll.

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    31
    Rep Power
    0

    Re: outdoor fan not starting

    I would check with manufacturer as to what outdoor temp the unit will operate at as europe has had a very cold winter.

  4. #4
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: outdoor fan not starting

    hi
    1-pipe sensor is faulty
    2-u can fit a high pressure to control outside fan

  5. #5
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: outdoor fan not starting

    stojaan,
    The Mideas we get here are rated for outside maximum outdoor temp of,, -7c. only.maybe too cold for them there.

  6. #6
    Join Date
    Feb 2010
    Location
    sofia bulgaria
    Posts
    3
    Rep Power
    0

    Re: outdoor fan not starting

    Hello Stojaan, can you measured resistance of pipe sensor of indor unit ( in 25℃ resistance is 10 KΩ ) If you want send me e-mail with model and I give you service manual. boris_sofia@yahoo.com

  7. #7
    Join Date
    Nov 2009
    Location
    Krumovgrad town
    Age
    45
    Posts
    2
    Rep Power
    0

    Re: outdoor fan not starting

    It's a CSU12HHAA model, much appreciated if you could give me the manual!

Similar Threads

  1. may tag refrigerator starting problem
    By wouellet in forum Domestic
    Replies: 3
    Last Post: 22-12-2009, 08:15 AM
  2. starting a small market
    By bruce113113 in forum Supermarket Refrigeration
    Replies: 3
    Last Post: 30-09-2009, 02:12 AM
  3. First starting off
    By marc5180 in forum Legal-Business-Marketing
    Replies: 7
    Last Post: 08-10-2007, 05:51 PM
  4. starting of defrost time
    By pirestani in forum New Technologies
    Replies: 6
    Last Post: 28-06-2006, 04:11 PM
  5. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •