    3 Phase Electric Heat Strips



    We have a auditorium with a split system. Two condensors on the roof twinned to one air handler in a mechanical off the auditorium.

    The air handler is equipped with two 15 kw heat strips. The problem we are having is when the unit is running with the heat strips only we can check the supply temp just past the strips and we are only reading 75-76 degree heat.

    The supply is reading 67-68. We have an amp draw of 11 amps each strip. We have outdoor dampers but they are closed with only a small amount of outside air slipping past.

    Any suggestions?



  2. #2
    Join Date
    Feb 2010
    Location
    USA
    Age
    56
    Posts
    8
    Rep Power
    0

    Re: 3 Phase Electric Heat Strips

    Additional information.

    I would like some information on how to electrically troubleshoot a 3 phase 460 volt heater.

  3. #3
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: 3 Phase Electric Heat Strips

    If you electriclly isolate the heaters and then measure the resistance of each heater element or group of elements. Once you have this reading, along with the current being draen by each element or group of elements, you should be able to apply Ohms Law from which you will be able to calculate the expected current. V/I=R and W=V*I. Where V=volts, I=current , R=resistance and W=watts. If this is not confirmed by the actual current drawn, then you possibly have a faulty element. If one of the elements has a different resistance, then this could be the faulty one. Proceed carefully and do not jump to a conclusion.

  4. #4
    Join Date
    Feb 2010
    Location
    NEWARK NJ
    Posts
    5
    Rep Power
    0

    Re: 3 Phase Electric Heat Strips

    sounds like heaters are not 100% for 15kw, check overloads they may be weak and cutting out.

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: 3 Phase Electric Heat Strips

    You can also check the currant draw with clamp Ampere meter and get the state of the heating stripes strait away.

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: 3 Phase Electric Heat Strips

    Quote Originally Posted by wrangoth View Post
    The air handler is equipped with two 15 kw heat strips. The problem we are having is when the unit is running with the heat strips only we can check the supply temp just past the strips and we are only reading 75-76 degree heat.

    The supply is reading 67-68. We have an amp draw of 11 amps each strip. We have outdoor dampers but they are closed with only a small amount of outside air slipping past.
    11amps per strip doesn't mean anything unless we know the voltage.

    The temperature rise across a heater battery is also dependant on the air volume passing over it.

    Do you know the airflow?

  7. #7
    Join Date
    Feb 2010
    Location
    USA
    Age
    56
    Posts
    8
    Rep Power
    0

    Re: 3 Phase Electric Heat Strips

    I really need a good explanation for troubleshooting a 3 phase heater.

    I have no problem with single phase but the 3 phase confuses me.

    1. Should all legs of the heater have identical ohm readings? Is it a must to disconnect the wiring before ohming it? If ohms read different, is that a sure indicator that the heater is bad?

    2. Should all legs have identical amp readings? On this unit each leg is getting the same voltage.

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: 3 Phase Electric Heat Strips

    Quote Originally Posted by wrangoth View Post
    I really need a good explanation for troubleshooting a 3 phase heater.

    I have no problem with single phase but the 3 phase confuses me.

    1. Should all legs of the heater have identical ohm readings? Is it a must to disconnect the wiring before ohming it? If ohms read different, is that a sure indicator that the heater is bad?

    2. Should all legs have identical amp readings? On this unit each leg is getting the same voltage.
    3 phase heaters are connected in Y arrangement.
    From one side, all the legs are connected to 0 and the other 3 legs are connected to to the 3 phases.

    As I've said before, switch it on and check with clamp ampere meter, on a faulty heater, you will get different reading.
    If Ω's is what you are after, then disconnect each heater for accurate reading.

  9. #9
    Join Date
    Feb 2010
    Location
    USA
    Age
    56
    Posts
    8
    Rep Power
    0

    Re: 3 Phase Electric Heat Strips

    Thanks. I checked each leg with the amp meter and found one with no amperage. It is a 30 kw heater but it has 4 7.5 kws in the circuit. Two are piggy backed to make one heater.

    One heater was not working. Thus the low temp rise. Thank you.

  10. #10
    Join Date
    Feb 2010
    Location
    NEWARK NJ
    Posts
    5
    Rep Power
    0

    Re: 3 Phase Electric Heat Strips

    A basic 3 phase 15 kw heater at 240v should draw 40 amps

  11. #11
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: 3 Phase Electric Heat Strips

    If 460 VAC heaters try delta connection and really start heating, so long as supply and protection and air flow can handle load.
    magoo

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. Basics or is it?
    By Fett in forum Fundamentals
    Replies: 17
    Last Post: 10-09-2009, 01:45 AM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Replies: 5
    Last Post: 04-01-2008, 05:11 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •