Are standard mini splits like a mhi hyperinverter or hitatchi summit fitted with crankcase heaters?If so how many watts are they consuming when the units are off and are they regardless of ambient temperatures?
Are groundsource heatpumps fitted with these and is the parasitic standby consumption calculated into the viability/cop
14-02-2010, 10:48 PM #2
Re: Crankcase heater?
I've never worked on that kit but standard crank case heaters normally consume 70 -100w
Marc
14-02-2010, 11:02 PM #3
it is a terrible negative to heat pumps that isnt marketed. i shall pm a guy on moneysaving expert that has an energy meter hooked up to a hyperinverter to see what it is drawing.
15-02-2010, 01:06 AM #4
After a few google searches it seems many manufacturers have dropped crankcase heaters or reduced their watts.
http://www.mhiaa.com.au/docs/MHIAA15...2009%20WEB.pdf
This is only a 20 watter on upto a 16kw heatpump
see page 10
Some of the diakins are 50wattts,makes one wonder!
15-02-2010, 07:09 PM #5
You can always disconnect it from the circuit. IMEO if a compressor is required to operate on a regular basis even during harsh weather, there is no need for a heater. Frankly for all but the most severe conditions when the unit has not operated for some time (think car left in snow for a week and then asked to start), crankcase heaters are simply .not necessary
15-07-2010, 08:49 AM #6
Crankcase heater is a needed component in the heat pump, no matter what kind of heat pump.
The electricity of crankcase heater is 40 to 70w, and when compressor works, it is disconnected from the power. And some HP program design when the compressor exposed temperature is high than some degrees(for example 15 degrees), the crankcase heater is always disconnected.
15-07-2010, 11:48 AM #7
Up to 5TR Capacity In general Crankcase Heaters are not used. In bigger systems where the refrigerant charge is exceeding the limit and no Liquid solenoid valve provided to arrest the refrigerant migration Crank case Heater is must regardless of the off time and Ambient.
15-07-2010, 08:30 PM #8
The latest inverter driven compressors trickle a small current through the windings in the off condition to produce heat and prevent liquid migration, instead of using the conventional crankcase heater. The current is controlled by the electronic circuits, and is only produced based on certain parameters, i.e. not all the time.
15-07-2010, 10:14 PM #9
19-07-2010, 12:57 PM #10
Alot of units as Frank points out do not now use crankcase heaters at all but instead use a trickle current, when measuring standby power consumption on inverter driven units it is important not to use clamp meters but to instead use a watt hour meter in order to get correct readings. Also the manufacturers compressor heating strategy will need to be accounted for in order to then work out energy consumption and running costs. compressor warming really dosent account for much energy usage at all, we are talking about the same as a 60W light being switched on for 15 - 20 minutes every hour.
20-06-2011, 07:38 PM #11
I know these postings are really quite old but are really relevant to an ongoing issue I have with Altherma High Temperature 16 kw Heat Pump. Its standby power consumption is 200 w per hour, every hour - it never changes regardless of outside temperature etc. From above doesn't sound right - is it right it should do this?
Any words of wisdom much apprecieated. tks.
09-07-2011, 03:23 PM #12
RS21 Main Defrost Heater Help Please
By elnno in forum DomesticReplies: 1Last Post: 28-06-2009, 01:14 PM -
Single pole contactor & crankcase heater
By herefishy in forum Air ConditioningReplies: 7Last Post: 01-04-2009, 08:38 AM -
Whirpool defrost heater
By frozen fred in forum DomesticReplies: 0Last Post: 27-01-2008, 07:41 AM -
crankcase heater thought
By philjd26 in forum Trouble ShootingReplies: 25Last Post: 30-06-2007, 10:46 PM -
Crankcase heaters on splits?
By Makeit go Right in forum Air ConditioningReplies: 9Last Post: 12-06-2007, 08:16 PM