Could someone refer to a thread/ information where DX system with few evaporators (a chiller and ice maker) with different evaporating temperature connected to a single compressor is discussed. Any help will be greatly appreciated.
Regards.
-
14-02-2010, 07:56 AM #2
Re: Multiple evaporating temperature with a single compressor
Danfoss has some literature about this.
Compressor selected for a capacity equal to both loads and evaporating at temperature of ice maker.
Evaporating pressure regulator on chiller room.
SV in both liquid lines to shut off each one separately.
Or you could use a VFD and run on low speed with your compressor when only chill room is needed and on High speed when icemaker is running. We have an application worknig this way.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
14-02-2010, 09:05 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Multiple evaporating temperature with a single compressor
Last edited by nike123; 14-02-2010 at 09:21 AM.
-
14-02-2010, 01:06 PM #4
Re: Multiple evaporating temperature with a single compressor
Peter and Nike thank you so much.
-
17-02-2010, 09:06 PM #5
-
19-02-2010, 09:26 PM #6
Re: Multiple evaporating temperature with a single compressor
Well even it is an OLD post... I remember a clever set up that had in mind to reduce cost... But reducing cost also means reduce failures and problems since use less parts.
Well connect the icemakers evaporator first and the chiller second. At the output of the chiller connect a thermosat that would do the job...
Of course each evaporator would have its own line but the same return. Even I am sure that with the same supply line would work perfect as the return gas of an icemaker at 20C Temp is more or less -2C~-5C... So it is a good temperature for the chiller...
The problem with this system is that when the icemaker's bin is full BUT the chiller has been used and increased water temp or vice versa the compressor Cannot work .
Or you have to add a 3way solenoid valve to cut the part that do not need to work...
-
07-05-2010, 12:59 PM #7
Similar Threads
-
Quick freezing of fresh products
By maxim971 in forum Technical SpeculationsReplies: 12Last Post: 18-09-2009, 11:06 PM -
High discharge temp
By paul_h in forum Air ConditioningReplies: 48Last Post: 06-05-2009, 11:10 AM -
Check discharge & evaporating temperature !
By oilzee in forum FundamentalsReplies: 5Last Post: 29-11-2008, 07:28 PM -
advantage of twin screw compressor over single screw compressor
By azzah in forum New to REReplies: 7Last Post: 23-09-2008, 09:24 AM -
Different between compressor MYCOM single stage and compressor booster
By thien nhat in forum CommercialReplies: 7Last Post: 13-12-2007, 06:31 PM