    Suction and liquid line



    Hi all

    I have come across a 2 door freezer with liquid line and suction line same size (both 3/8" but the compressor suction is 1/2") and it 's taking so long for the temperature to drop down. Any ideas?



  2. #2
    Join Date
    May 2007
    Location
    Scotland
    Posts
    327
    Rep Power
    17

    Re: Suction and liquid line

    Whereabouts exactly is the suction 3/8''? Also, what are the arrangements for the expansion device, what is your superheat / subcooling, and dT across evap and condenser?

  3. #3
    Join Date
    Feb 2010
    Location
    NT
    Posts
    66
    Rep Power
    15

    Re: Suction and liquid line

    Hi mate,

    i have rectify this problem, suction line was too small...the dropper pipe from the evaporator to the condensing unit was too small, was 3/8". There was pressure drop. i have increase it to 1/2" and i'm getting a better flow of suction vapour.
    thanks to reply