11-02-2010, 09:32 PM #1
Daikin VRV
I'm having a problem with an: rsey10kly1 outdoor. The ambient sensor is reading 35c in an ambient of 5c, it's not high enough to trigger a fault yet unit won't heat as it thinks the ambient is too high.
I've swapped the probe with a good one, no joy, could there be anything else "dragging" this value out or is it a case of a board replacement?
PS
i wish it was 35c.............
alec
-
11-02-2010, 10:33 PM #2
Re: Daikin VRV
Hi Al,
How are you checking the thermistor value? By connecting service checker or by resistance reading.
Have you defiantly connected a thermistor with correct range?
5 C = 51Kohms
35 C = 13Kohms
Could be poor BCB connection or plug on PCB is loose (fractured solder connection) or as you said the PCB.
-
12-02-2010, 01:37 PM #3
Re: Daikin VRV
Hi VRV
I took an ambient sensor from another unit, both my sensors read OK on the good unit.
I'm just measuring the resistance at the moment, plucking up the courage (and the time) to follow the directions in the manual to check with the leds.
Is the service checker a worthwhile investment do you think?
Alec
-
12-02-2010, 06:05 PM #4
Re: Daikin VRV
Hi Alec,
What are you trying to do with LED’s? You can’t do anything with them that would be of an advantage for fault finding a thermistor error on K series VRV.
If you do a lot of work on Daikin equipment a service checker if defiantly worth while for checking and fault finding systems (once you're familiar with it).
-
12-02-2010, 11:35 PM #5
Re: Daikin VRV
i've ordered up a new pcb, can the leds be used to give real time info pressures etc while unit is running, or is it worth the hassle?
Thanks for the replies VRV
Alec
-
15-02-2010, 08:34 PM #6
Re: Daikin VRV
Hi Alec,
The outdoor push buttons and LED’s can be used to obtain some basic system info i.e. No. of indoors connected, No. of BS boxes connected and unit auto address etc. But you can not read real time operation data.
On newer 410a units they can also used for fault finding.
In setting mode 2 they are used to adjust outdoor field settings and activate service functions.
-
16-02-2010, 09:12 PM #7
Re: Daikin VRV
Thanks VRV, i'm back there next week, i reckon the board should do it.
BTW is it possible to get a service checker with out doing a Daikin course?
Alec
-
16-02-2010, 09:45 PM #8
Similar Threads
-
Daikin not working... many problems
By stankovicv in forum Air ConditioningReplies: 26Last Post: 11-12-2010, 09:01 AM -
Daikin, Why do we bother?
By gwilliamson in forum Air ConditioningReplies: 21Last Post: 02-02-2010, 09:38 AM -
Daikin AC parts from UK
By skel00 in forum Air ConditioningReplies: 5Last Post: 05-04-2009, 01:24 PM -
Fixing Daikin A3 Error
By Stuffy in forum Air ConditioningReplies: 3Last Post: 27-03-2009, 06:02 AM -
Daikin Comp and inverter
By WCC73 in forum Air ConditioningReplies: 5Last Post: 08-11-2008, 08:44 PM