    Re: TEV on long liquid line, liquid hammer



    Practically pressure from liquid would be approx 10barg at 20C ambient, so pressure pulses would less.
    What Chef calcs did prove was pressure spikes sure can be a problem (breaking of piping) a common problem!
    I would hope the client has installed an Alarm system, surely he did not loose product a second time?
    There are thousands of system with long pipes runs as you have described.
    (I remember Littlewoods systems were always like this 25 years ago, much longer pipe runs)
    In court, I do not know how you can prove negligence. It may not be a perfect design, but what is!
    On the original call the tech, added 60Kgs of refrigerant (seems like alot), was it removed. maybe there was a leak, some moisture had been drawn in causing the valves to block. No reduction it temp.
    Was a leak found, were driers replaced at each service call (technical should always be done)
    this you can find on the service invoices.
    You can not blame the tech for the first lot of product lose, as already unfrozen before he arrived.



  2. #52
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: TEV on long liquid line, liquid hammer

    I have 1 week time to give my report and I will add this as an additional advice. Thanks for you ongoing support you both.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  3. high liquid line pressure?
    By TECH TIM in forum Commercial
    Replies: 5
    Last Post: 09-05-2009, 05:36 PM
  4. liquid return through suction line after hot gas defrost period
    By coldkeeper1 in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 19-06-2008, 10:07 PM
  5. subcooling liquid line
    By mac_J in forum Technical Discussions
    Replies: 6
    Last Post: 15-02-2008, 10:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •