Thread: Carrier 30GH245
    Feb 2010
    Bulgaria
    36
    Carrier 30GH245
    Hello !
    I write for first time in this forum .
    I have wonder if someone can tell me the answer.
    I have a Carrier Air cooled chiller , Model 30GH245
    800 KW cooling power , with 8 reciprocating semi-hermetic compressors 06E. 2 circuits and Refrigerant R22.
    Can this chiller be using for ice rink somehow ?
    The ice rink need about -4 , -5 degrees .
    Thanks in advance !
    Split Croatia
    57
    6,151
    36
    Re: Carrier 30GH245
    I generally don't see reason why not for any chiller if you use glycol solution and you are within operating envelope of compressor.
    http://www.carlylecompressor.com/Fil...ngEnvelope.pdf
    11,025
    Re: Carrier 30GH245
    Documentation if you need it...
    http://eto.carrier.com/lit.asp
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2008
    u.a.e
    49
    412
    23
    Re: Carrier 30GH245
    [quote=narkom;177220]
    Quote Originally Posted by yanev22;177141
    /quote
    For ice rink application glycol leaving temperature must be -8C during freezing. And -4, -5C to hold about 15mm thickness of ice. So you should expect the evap. pressure is from 2 to 2.3 bar and check LP protection of the chiller.
    30 GH chiller can’t use for low temperature. This has designed for comfort cooling. It has programmed setting in accordance the medium temp. Applications. Especially 06E compressor for only medium or high temperature applications.06CC compressor using for low temp.
    Moideen-Dubaifficeffice" />>>
  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. carrier 30gx oil separator heaters
    By Coolie in forum Trouble Shooting
    Last Post: 12-05-2010, 05:58 PM
  3. Carrier Chillers
    By Ed Burris in forum Technical Discussions
    Last Post: 27-03-2010, 02:00 AM
  4. Geoff in NY ~ Carrier Parts
    By Futsal1st in forum Trouble Shooting
    Last Post: 30-12-2009, 04:07 AM
  5. Help identifying carrier HiWall dom. split
    By paul_h in forum Air Conditioning
    Last Post: 12-12-2008, 09:12 AM