    Carrier 30GH245



    Hello !

    I write for first time in this forum .

    I have wonder if someone can tell me the answer.

    I have a Carrier Air cooled chiller , Model 30GH245
    800 KW cooling power , with 8 reciprocating semi-hermetic compressors 06E. 2 circuits and Refrigerant R22.

    Can this chiller be using for ice rink somehow ?
    The ice rink need about -4 , -5 degrees .

    Thanks in advance !



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Carrier 30GH245

    I generally don't see reason why not for any chiller if you use glycol solution and you are within operating envelope of compressor.
    http://www.carlylecompressor.com/Fil...ngEnvelope.pdf

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Carrier 30GH245

    Documentation if you need it...
    http://eto.carrier.com/lit.asp
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: Carrier 30GH245

    [quote=narkom;177220]
    Quote Originally Posted by yanev22;177141

    Can this chiller be using for ice rink somehow ?
    The ice rink need about -4 , -5 degrees .
    /quote

    For ice rink application glycol leaving temperature must be -8C during freezing. And -4, -5C to hold about 15mm thickness of ice. So you should expect the evap. pressure is from 2 to 2.3 bar and check LP protection of the chiller.
    30 GH chiller can’t use for low temperature. This has designed for comfort cooling. It has programmed setting in accordance the medium temp. Applications. Especially 06E compressor for only medium or high temperature applications.06CC compressor using for low temp.

    Moideen-Dubaifficeffice" />>>

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. carrier 30gx oil separator heaters
    By Coolie in forum Trouble Shooting
    Replies: 6
    Last Post: 12-05-2010, 05:58 PM
  3. Carrier Chillers
    By Ed Burris in forum Technical Discussions
    Replies: 6
    Last Post: 27-03-2010, 02:00 AM
  4. Geoff in NY ~ Carrier Parts
    By Futsal1st in forum Trouble Shooting
    Replies: 6
    Last Post: 30-12-2009, 04:07 AM
  5. Help identifying carrier HiWall dom. split
    By paul_h in forum Air Conditioning
    Replies: 4
    Last Post: 12-12-2008, 09:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •