    Apr 2006
    Northern Ireland
    31
    Talking Lighting circuit trips when heat pump starts
    We have a 15.95kW 1ph 230V 50hz GSHP, which is connected to the power fuse board that has 30 ma RCCB.
    It starts up and runs fine.
    There is a fuse board for lights, which has a 100ma RCCB, near the power fuse board. The fuse boards are completely separate, the earths are neutralised.
    When the heat pump starts up, the 100ma RCCB trips, but when it is reset it stays connected.
    Any comments and advice appreciated
    3,856
    Re: Lighting circuit trips when heat pump starts
    I do some work on a farm and when they have any major electrical problems, shorts and such, it used to trip the power in a house about 500 yards away, was told it was due to the chalky ground.
    What this has to do with you problem i don't know, goes back to glass of scotch
    Mar 2009
    KZN, South Africa
    64
    2,212
    Quote Originally Posted by mac_J View Post
    Does the heat-pump have a soft starter? If not, then you may want to consider installing one.
    Jan 2010
    wales
    56
    55
    15
    could you tell us if the 30ma rcd is working correctly as it been tested
    Split Croatia
    57
    6,151
    36
    Maybe because of this ( fig. 24 if I correctly interpreted your description):
  1. Capacity control
    By sparrow in forum Training
    Last Post: 18-01-2010, 07:49 PM
  2. Calorex 510 Heat pump question
    By jugglerb in forum Heat Pumps
    Last Post: 21-06-2009, 10:49 AM
  3. Sizing of Heat pump
    By pinkpanther in forum Tools and Calculators
    Last Post: 24-05-2009, 08:16 PM
  4. Homemade Heat Pump...
    By AC_Hacker in forum New to RE
    Last Post: 29-04-2009, 11:30 PM
  5. Will this heat pump work?
    By goodguy in forum Heat Pumps
    Last Post: 08-03-2008, 04:14 PM