Lighting circuit trips when heat pump starts
We have a 15.95kW 1ph 230V 50hz GSHP, which is connected to the power fuse board that has 30 ma RCCB.
It starts up and runs fine.
There is a fuse board for lights, which has a 100ma RCCB, near the power fuse board. The fuse boards are completely separate, the earths are neutralised.
When the heat pump starts up, the 100ma RCCB trips, but when it is reset it stays connected.
Any comments and advice appreciated
Regards
-
08-02-2010, 12:25 AM #2
Re: Lighting circuit trips when heat pump starts
I do some work on a farm and when they have any major electrical problems, shorts and such, it used to trip the power in a house about 500 yards away, was told it was due to the chalky ground.
What this has to do with you problem i don't know, goes back to glass of scotch
-
08-02-2010, 02:49 AM #3
-
08-02-2010, 08:46 PM #4
Re: Lighting circuit trips when heat pump starts
could you tell us if the 30ma rcd is working correctly as it been tested
-
08-02-2010, 10:03 PM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Lighting circuit trips when heat pump starts
Maybe because of this ( fig. 24 if I correctly interpreted your description):
Last edited by nike123; 08-02-2010 at 10:06 PM.
Similar Threads
-
Capacity control
By sparrow in forum TrainingReplies: 44Last Post: 18-01-2010, 07:49 PM -
Calorex 510 Heat pump question
By jugglerb in forum Heat PumpsReplies: 8Last Post: 21-06-2009, 10:49 AM -
Sizing of Heat pump
By pinkpanther in forum Tools and CalculatorsReplies: 5Last Post: 24-05-2009, 08:16 PM -
Homemade Heat Pump...
By AC_Hacker in forum New to REReplies: 0Last Post: 29-04-2009, 11:30 PM -
Will this heat pump work?
By goodguy in forum Heat PumpsReplies: 7Last Post: 08-03-2008, 04:14 PM