    Heat Reclaim from a 9 kw a Copeland Scroll Condensing unit



    What is the best arrangement for using the Discharge Super Heat to heat domestic hot water.

    We have a 9 kW copeland Scroll air cooled condensing unit using R404a on a milk cooling ice bank.

    What is the best type of Refrigerant to Water heat changer to use?

    Would a Fan speed controller be needed?

    All comments and advice appreciated.

    Regards



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Heat Reclaim from a 9 kw a Copeland Scroll Condensing unit

    Have a look here. This kind of units will do the job for you.

    Speed controller or pressure control for the fans is needed.

    http://www.eurekaheatrecovery.co.uk/index.php

  3. #3
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Heat Reclaim from a 9 kw a Copeland Scroll Condensing unit

    Or these guys, very efficient on smaller condensing units down to 1hp for pubs etc.http://www.dk-kaelteanlagen.de/

    alec

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Heat Reclaim from a 9 kw a Copeland Scroll Condensing unit

    I've fitted a Fabdec heat recovery on a Mueller dx, only about 3000L, was really impressed, comp was about 5 or 6 hp and heat reco tank was about 300L and you could stand and watch the temperature go up on it, it was the sole source of hot water for tank washing with no electric top up.

    Ideally you'd need to fit a fan speed control, a discharge pipe muffler and some bypass valves. But the one i fitted only had a muffler (needed to for the warranty from Fabdec) as it was suppplied and spec'd by the milking parlour guy.

    Jon

  5. #5
    Join Date
    Apr 2006
    Location
    Northern Ireland
    Posts
    31
    Rep Power
    0

    Re: Heat Reclaim from a 9 kw a Copeland Scroll Condensing unit

    Thanks Chemi-cool

    I have checked out the Eureka Heat Recovery Systems web site

    Have to check which is it best to pre cool the milk with bore hole water.

    This would reduce the refrigeration load by at least 60%.

    Or to use the Discharge Super heat to produce hot water, with out any pre cooling of the milk.

    Maybe pre cool and recover less super heat for heat the water.

    Any thoughts

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Heat Reclaim from a 9 kw a Copeland Scroll Condensing unit

    Pre cool the milk first and use the water for volume washing the parlour and drinking water for the cows, they'll drink more if its warm, so i'm told. Its free cooling!

    Then use the fridge system to cool the milk and pre heat the water for plant and tank washing.

    There was an article on it in the farmers weekly a few months back, no actual figures but the farmer said he was saving on run time on the fridge system and electric on water heating, had four units connected to heat recovery, two on dx tank and two on ice builder.
    Last edited by monkey spanners; 07-02-2010 at 10:34 PM. Reason: more info!

  7. #7
    Join Date
    Apr 2006
    Location
    Northern Ireland
    Posts
    31
    Rep Power
    0

    Re: Heat Reclaim from a 9 kw a Copeland Scroll Condensing unit

    Thanks for all the information

  8. #8
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Heat Reclaim from a 9 kw a Copeland Scroll Condensing unit

    Quote Originally Posted by chemi-cool View Post
    Have a look here. This kind of units will do the job for you.

    Speed controller or pressure control for the fans is needed.

    http://www.eurekaheatrecovery.co.uk/index.php
    A very nice, simple system, chemi. Thanks for that link.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  9. #9
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Heat Reclaim from a 9 kw a Copeland Scroll Condensing unit

    Quote Originally Posted by monkey spanners View Post
    Pre cool the milk first and use the water for volume washing the parlour and drinking water for the cows, they'll drink more if its warm, so i'm told. Its free cooling!

    Then use the fridge system to cool the milk and pre heat the water for plant and tank washing.

    There was an article on it in the farmers weekly a few months back, no actual figures but the farmer said he was saving on run time on the fridge system and electric on water heating, had four units connected to heat recovery, two on dx tank and two on ice builder.
    Hi Monkey, you have brought about water usage after pre-cooling "Cows drinking more" many moons ago there was a lot of research on this, it was found that cows do prefer to drink warm water, but it was also found that some cows are more inteligent than others. The smarter cows would only drink around milking time (warm water), milk production fell.
    So the big question for the farmer, are his cows bright or not.

    As far as heat recovery goes, there are many ways to skin a cat.
    One of the major problems, is pressure drops in the discharge (with desuperheaters). This can adversely efffect the running of the refrigeration unit. (high head pressures), this is very rarely seen, as when we look at the plants the water being heated is normally cold. As the water warms "the shrinking effect" on the discharge refrigerant reduces. The shrinkage (contraction) over comes the heat exchanges natural pressure drop.

    Do you work for Harry Noblet?

  10. #10
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Heat Reclaim from a 9 kw a Copeland Scroll Condensing unit

    Quote Originally Posted by mad fridgie View Post
    Hi Monkey, you have brought about water usage after pre-cooling "Cows drinking more" many moons ago there was a lot of research on this, it was found that cows do prefer to drink warm water, but it was also found that some cows are more inteligent than others. The smarter cows would only drink around milking time (warm water), milk production fell.
    So the big question for the farmer, are his cows bright or not.

    As far as heat recovery goes, there are many ways to skin a cat.
    One of the major problems, is pressure drops in the discharge (with desuperheaters). This can adversely efffect the running of the refrigeration unit. (high head pressures), this is very rarely seen, as when we look at the plants the water being heated is normally cold. As the water warms "the shrinking effect" on the discharge refrigerant reduces. The shrinkage (contraction) over comes the heat exchanges natural pressure drop.

    Do you work for Harry Noblet?
    Harry Noblet, now theres a name i haven't heard for years!
    I'm self employed now but used to work for a main agent of milk tanks, who used to sell to Noblet refrigeration. I seem to remember one of his rusty looking transit vans being parked in our yard when my boss took some dealers on a trip to the factory

    Jon

Similar Threads

  1. Air source heat pump – high temp unit or not?
    By aa44 in forum Fundamentals
    Replies: 14
    Last Post: 26-09-2010, 09:08 PM
  2. DX capacity lower than condensing unit
    By M.Saleh in forum Trouble Shooting
    Replies: 5
    Last Post: 17-01-2010, 09:29 PM
  3. Basics or is it?
    By Fett in forum Fundamentals
    Replies: 17
    Last Post: 10-09-2009, 01:45 AM
  4. York/Bristol Condensing Unit
    By Abe in forum Commercial
    Replies: 1
    Last Post: 03-02-2003, 07:46 PM
  5. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •