    low discharge temperaure



    hi everyone
    i just want to know the reasons that may cause low discharge temperature when using a screw compressor
    please help me
    best regards



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: low discharge temperaure

    low suction superheat, high evaporating pressure and low condensing pressure (low pressure ratio)

  3. #3
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: low discharge temperaure

    Hi Reyad,

    Was curious to hear about your specific problem, was the compressor fully loaded when you monitored the discharge temperature, how about a liquid injection problem? amongst the many scenarios.

    Cheers
    Tutto il Mondo e un Paese

  4. #4
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    48
    Posts
    184
    Rep Power
    20

    Re: low discharge temperaure

    Hi,

    You have to tell us other things like the pressure which is versus the "low discharge temperature", the type of refrigerant used and the application of the refrigeration system. I always tell other people that refrigeration and airconditioning is a science and figures (numbers) are what you need to reach a conclusive decision when it comes to problem resolution.
    Last edited by PRESS; 06-02-2010 at 09:04 PM.

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: low discharge temperaure

    Hi, reyad-saleh

    Quote Originally Posted by reyad-saleh View Post
    hi everyone
    i just want to know the reasons that may cause low discharge temperature when using a screw compressor
    please help me
    best regards
    possible oil cooler is not working well ... cooling oil too much .... then liquid on compressor suction ...

    sorry not enough input data .... we can only guess ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  6. #6
    bkargol's Avatar
    bkargol Guest

    Re: low discharge temperaure

    it all points to problems in the evaporator, the low discharge superheat is an indication of refrigerant carryover, over charged, low chilled water flow, fouled tubes, or anything which would not allow the evaporation of refrigerant in the cooler, there are many other things but as mentioned by others much more info is needed,

  7. #7
    Join Date
    Mar 2010
    Location
    UTAH
    Posts
    24
    Rep Power
    0

    Re: low discharge temperaure

    That Really helped me too... nice posts..

Similar Threads

  1. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  2. Replies: 5
    Last Post: 08-11-2009, 05:10 PM
  3. High discharge temp
    By paul_h in forum Air Conditioning
    Replies: 48
    Last Post: 06-05-2009, 11:10 AM
  4. Stal discharge check rattle mystery
    By Howeirdhughs in forum Trouble Shooting
    Replies: 5
    Last Post: 16-12-2008, 08:21 AM
  5. Exploded discharge line
    By Peter_1 in forum Industrial
    Replies: 1
    Last Post: 05-05-2004, 09:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •