06-02-2010, 06:33 PM #1
low discharge temperaure
hi everyone
i just want to know the reasons that may cause low discharge temperature when using a screw compressor
please help me
best regards
-
06-02-2010, 07:32 PM #2
Re: low discharge temperaure
low suction superheat, high evaporating pressure and low condensing pressure (low pressure ratio)
-
06-02-2010, 08:43 PM #3
Re: low discharge temperaure
Hi Reyad,
Was curious to hear about your specific problem, was the compressor fully loaded when you monitored the discharge temperature, how about a liquid injection problem? amongst the many scenarios.
CheersTutto il Mondo e un Paese
-
06-02-2010, 08:57 PM #4
Re: low discharge temperaure
Hi,
You have to tell us other things like the pressure which is versus the "low discharge temperature", the type of refrigerant used and the application of the refrigeration system. I always tell other people that refrigeration and airconditioning is a science and figures (numbers) are what you need to reach a conclusive decision when it comes to problem resolution.Last edited by PRESS; 06-02-2010 at 09:04 PM.
-
05-03-2010, 09:49 PM #5
Re: low discharge temperaure
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
05-03-2010, 10:03 PM #6
Re: low discharge temperaure
it all points to problems in the evaporator, the low discharge superheat is an indication of refrigerant carryover, over charged, low chilled water flow, fouled tubes, or anything which would not allow the evaporation of refrigerant in the cooler, there are many other things but as mentioned by others much more info is needed,
-
08-03-2010, 11:12 AM #7
Re: low discharge temperaure
That Really helped me too... nice posts..
Similar Threads
-
Carrier 23xl chiller-Low discharge superheat alarms
By Bradysmill in forum Trouble ShootingReplies: 7Last Post: 25-04-2010, 07:43 PM -
19XL High Discharge Temp intermittent alarm at compressor start
By pete_d in forum CommercialReplies: 5Last Post: 08-11-2009, 05:10 PM -
High discharge temp
By paul_h in forum Air ConditioningReplies: 48Last Post: 06-05-2009, 11:10 AM -
Stal discharge check rattle mystery
By Howeirdhughs in forum Trouble ShootingReplies: 5Last Post: 16-12-2008, 08:21 AM -
Exploded discharge line
By Peter_1 in forum IndustrialReplies: 1Last Post: 05-05-2004, 09:47 PM