    Oct 2009
    Syria
    low discharge temperaure
    hi everyone
    i just want to know the reasons that may cause low discharge temperature when using a screw compressor
    please help me
    best regards
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: low discharge temperaure
    low suction superheat, high evaporating pressure and low condensing pressure (low pressure ratio)
    Britain
    220
    Hi Reyad,
    Was curious to hear about your specific problem, was the compressor fully loaded when you monitored the discharge temperature, how about a liquid injection problem? amongst the many scenarios.
    Tutto il Mondo e un Paese
    Republic of south africa
    49
    184
    You have to tell us other things like the pressure which is versus the "low discharge temperature", the type of refrigerant used and the application of the refrigeration system. I always tell other people that refrigeration and airconditioning is a science and figures (numbers) are what you need to reach a conclusive decision when it comes to problem resolution.
    Croatia
    68
    2,263
    Hi, reyad-saleh
    Quote Originally Posted by reyad-saleh View Post
    hi everyone
    please help me
    best regards
    possible oil cooler is not working well ... cooling oil too much .... then liquid on compressor suction ...
    sorry not enough input data .... we can only guess ...
    Best regards, Josip
    bkargol's Avatar
    bkargol Guest
    it all points to problems in the evaporator, the low discharge superheat is an indication of refrigerant carryover, over charged, low chilled water flow, fouled tubes, or anything which would not allow the evaporation of refrigerant in the cooler, there are many other things but as mentioned by others much more info is needed,
    Mar 2010
    UTAH
    That Really helped me too... nice posts..
  1. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Last Post: 25-04-2010, 07:43 PM
  2. Replies: 5
    Last Post: 08-11-2009, 05:10 PM
  3. High discharge temp
    By paul_h in forum Air Conditioning
    Last Post: 06-05-2009, 11:10 AM
  4. Stal discharge check rattle mystery
    By Howeirdhughs in forum Trouble Shooting
    Last Post: 16-12-2008, 08:21 AM
  5. Exploded discharge line
    By Peter_1 in forum Industrial