Results 1 to 13 of 13
    Oct 2009
    Syria
    45
    liquid in the suction line
    hi all
    could you tell me what i can do if i get liquid in the suction line of a screw compressor.
    thank you very much
    scotland
    756
    Re: liquid in the suction line
    firstly find out why its getting there i,e stuck solenoid valve or akv,then fix it, then the tricky bit either reclaim it or allow the compressor to pull it out try shutting the suction valve at the compressor,then crack it open ever so slightly and let the comp pull it back, just keep a eye on the oil level.
    Jul 2009
    Brisbane
    67
    79
    15
    What type of system is it? Is it refrig or A/C? What is it operating at eg SST, cond temp etc. Is it dx or flooded. Is it a operating a chiller. What refrigerant and expansion device does it have. Does it have a header or accumulator? Many questions I know but it will help everyone to diagnose your problem more easily.
    Auckland
    74
    3,357
    37
    screws are faily tolerent with saturated suction gases, but liquid, not good. Something will break. More info on system application and refrigerant would be helpfull.
    magoo
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Apr 2008
    u.a.e
    49
    412
    23
    Quote Originally Posted by reyad-saleh View Post
    hi all
    thank you very much
    is this flooded or DX chiller?
    Moideen-Dubai
    Feb 2010
    NT
    66
    15
    what kind of system is it..
    Jan 2006
    Croatia
    68
    2,263
    31
    Hi, reyad-saleh
    hi all
    thank you very much
    find out if you get and why you get liquid in the suction line ... then remedy cause ....
    Best regards, Josip
    Feb 2010
    usa
    21
    Make sure you evaporate the liquid out of the T.
    nass's Avatar
    nass Guest
    there must be liquid slugging.check for overccharge and superheat at expansion valve..my email add is nassalish7861@yahoo.com
    May 2010
    ipswich
    31
    26
    very very rarly will you need to turn the skrew for the tx valve, you my need to close the tx valve because its letting to much refrigerant in. can be a dumb thing to do.. check your supper heat and an enthalpy chart my come in handy
    Dec 2010
    Fl,United States
    probably over charged, is it dx or txv?
    Feb 2010
    United Kingdom
    More information required. Probably an expansion valve issue. Has it got an accumulator on?
    Feb 2009
    14
    Is it a DX system - Evaporator blocked, iced, fans working?
  1. what is useful of Economizer?
    By Ahmed.ragab in forum Industrial Compressors
    Last Post: 18-08-2010, 12:15 PM
  2. Charging liquid through suction line?
    By SloFuse in forum Trouble Shooting
    Last Post: 20-06-2010, 09:26 PM
  3. high liquid line pressure?
    By TECH TIM in forum Commercial
    Last Post: 09-05-2009, 05:36 PM
  4. Suction and liquid line capacities for 410a
    By mac_J in forum Heat Pumps
    Last Post: 09-10-2007, 12:51 AM
  5. Bearing trouble - rotary compressor
    By rosetennis in forum Industrial Compressors
    Last Post: 18-05-2006, 01:26 AM