    Free air calculation.

    Hi all, I'm in the process of servicing an AHU system as part of a building refurb that our company is doing. Does anyone know roughly the free air area of a 600x600 4 way supply diffuser? You know the sort, aluminium painted white, that sits in t-bar ceiling grid.
    I need this to apply to my anemometer m/s readings to give client the volumes.
    I know they will vary by manufacturer but a ball park figure will help a lot.
    Thanks

  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Free air calculation.

    Best/easiest way is to make up a cardboard air collection hood, calibrate it and then take all of your readings with the hood.

    edit: Just checked with Lindab catalogue, they don't give free areas (damn). Looks like you'll have to measure the slots yourself.
    Last edited by Brian_UK; 05-02-2010 at 08:08 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jan 2010
    Location
    Ireland
    Age
    45
    Posts
    18
    Rep Power
    0

    Re: Free air calculation.

    Hello

    If the air distribution system incorporates a moderate number of air terminals, I would recommend hiring a propriety 'flow measuring hood' for the job. These instruments employ balometer technology to measure the volume flow rate and normally include digital displays with high resolution. It is important to examine the calibration certificate before you leave the store to verify the instruments accuracy. It can be very difficult to attain accurate and consistant readings without the appropriate equipment.
    Depending on the quantity of terminals to be measured, alot of time can be saved if you have an assistant to identify the terminal and record the respective flow rates while comparing against design figures.

    Hope this helps.

    Solas

  4. #4
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    745
    Rep Power
    25

    Re: Free air calculation.

    46% according to the downloads here

    ooooooPs, I've always used 60% in my calcs , my systems always work though.

    Eggs

  5. #5
    drmile's Avatar
    drmile Guest

    Re: Free air calculation.

    0.11m2
    Milenko

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Free air calculation.

    use an anomometer and a tape measure.
    Lineal metres flow x metres squared is total flow.
    Lots of lineal flow readings and average. Not rocket science stuff.

    magoo

  7. #7
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    745
    Rep Power
    25

    Re: Free air calculation.

    Quote Originally Posted by Magoo View Post
    Not rocket science stuff.
    magoo
    Neither is reading the question.

    Quote Originally Posted by coolhandlew View Post
    Does anyone know roughly the free air area of a 600x600 4 way supply diffuser?
    Eggs

  8. #8
    Join Date
    Dec 2008
    Location
    Isle of Man
    Age
    55
    Posts
    42
    Rep Power
    0

    Re: Free air calculation.

    Quote Originally Posted by Magoo View Post
    use an anomometer and a tape measure.
    Lineal metres flow x metres squared is total flow.
    Lots of lineal flow readings and average. Not rocket science stuff.

    magoo
    I'm well aware of that, but there has to be a correction factor for restrictions ie. louvres etc

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Free air calculation.

    For "eggs "and everyone else there is a standard for a difuser hood testing forget about louvers .., what ever comes out is actual, my initial comment stands.
    For commissioning a/c diffusers a square test hood that reduces from square to round with a fixed discharge diameter, add anemometer will give the actual flow rates, the angle from square to round to meet standard is 11 degrees. Then use calcultor and flow rates. Like I said earlier not rocket science. The more cross reference readings the better, increases the accurracy.
    Last edited by Magoo; 15-02-2010 at 02:53 AM.

Similar Threads

  1. how can we calculation industrial refrigeration
    By lam sanh in forum System Optimization
    Replies: 34
    Last Post: 28-02-2011, 02:31 PM
  2. fujitsu wall mount volt free relay
    By mike live in forum Air Conditioning
    Replies: 3
    Last Post: 09-04-2009, 08:26 PM
  3. Replies: 3
    Last Post: 27-11-2007, 11:00 AM
  4. frost free
    By sashy552 in forum Domestic
    Replies: 1
    Last Post: 22-06-2007, 11:20 PM
  5. oil free compressor
    By Lc_shi in forum Fundamentals
    Replies: 6
    Last Post: 22-10-2006, 01:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •