    Hi guys!
    I've just registered in this site. I have a huge problem here trying to design an airconditioning system for a computer equipment container.
    I worked out a plant capacity of 6.5kW, the ambient temperature being 40 deg C, room tempereature being 12 deg C with 75RH as see level.
    I selected a danfoss/maneurop compressor MT028-4 (R22 refr)with cooling capacity of 7.3kW, Power = 2.55kW, To=7.2deg C (satureted suction), Tc=54.4deg C (saturated discharge).
    According to my calculations, the THR at the condenser is: 6.5 + 2.55 = 9.05kW.
    I have calculated the TD condenser to be: 54.4 - 40 = 14.4 K. I plan to use a fan/fans with 2m/s air velocity.
    For the evaporator TD is: 12 - 7.2 = 4.8K. I plan to use a fan/fans with 2m/s air velocity.
    Now i want to calculate the area of the evap & condensor coils including the depth (number of rows).
    I was thinking that the this formula would help:
    Q = U . A. dT.
    Lets assume that both coils will be made from copper fins & tubes. I think the U factor can be looked up in the material specificifications. Change in temperature is already determined in TD. and Q is already calculated.
    I can obviously find the Area by making A the subject of the formula, but, now how do i know how deep the coils should be?
    I know that most coil manufacturers would have the software already to size all the components, but, i want to know how to work it out myself.
    Please help guys.
    jana's Avatar
    jana Guest
    Re: Complete aircon system design, help with sizing coils (evap & cond)
    Calculate the total external surface area of fins & tubing required to handle the heat transfer. Size the coil & number of passes from this total area.
    11,024
    12°C seems too cold for computer equipment, not a complaint, just interested.
  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Last Post: 21-03-2012, 10:09 PM
  2. Autocascade refrigeration system: design verification needed
    Last Post: 07-02-2010, 07:48 AM
  3. Replies: 35
    Last Post: 13-12-2006, 11:51 AM
  4. What is System balance?
    By shogun7 in forum Technical Speculations
    Last Post: 19-01-2006, 09:47 AM
  5. R507 in an R134a compressor: system design
    Last Post: 01-05-2003, 09:25 AM