Complete aircon system design, help with sizing coils (evap & cond)
Hi guys!
I've just registered in this site. I have a huge problem here trying to design an airconditioning system for a computer equipment container.
I worked out a plant capacity of 6.5kW, the ambient temperature being 40 deg C, room tempereature being 12 deg C with 75RH as see level.
I selected a danfoss/maneurop compressor MT028-4 (R22 refr)with cooling capacity of 7.3kW, Power = 2.55kW, To=7.2deg C (satureted suction), Tc=54.4deg C (saturated discharge).
According to my calculations, the THR at the condenser is: 6.5 + 2.55 = 9.05kW.
I have calculated the TD condenser to be: 54.4 - 40 = 14.4 K. I plan to use a fan/fans with 2m/s air velocity.
For the evaporator TD is: 12 - 7.2 = 4.8K. I plan to use a fan/fans with 2m/s air velocity.
Now i want to calculate the area of the evap & condensor coils including the depth (number of rows).
I was thinking that the this formula would help:
Q = U . A. dT.
Lets assume that both coils will be made from copper fins & tubes. I think the U factor can be looked up in the material specificifications. Change in temperature is already determined in TD. and Q is already calculated.
I can obviously find the Area by making A the subject of the formula, but, now how do i know how deep the coils should be?
I know that most coil manufacturers would have the software already to size all the components, but, i want to know how to work it out myself.
Please help guys.
-
04-02-2010, 05:53 PM #2
Re: Complete aircon system design, help with sizing coils (evap & cond)
Calculate the total external surface area of fins & tubing required to handle the heat transfer. Size the coil & number of passes from this total area.
-
04-02-2010, 06:38 PM #3
Re: Complete aircon system design, help with sizing coils (evap & cond)
12°C seems too cold for computer equipment, not a complaint, just interested.
Brian - Newton Abbot, Devon, UK
Retired March 2015
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
Autocascade refrigeration system: design verification needed
By DaBit in forum Technical SpeculationsReplies: 3Last Post: 07-02-2010, 07:48 AM -
System design: first cost or operating cost?
By US Iceman in forum NH3Replies: 35Last Post: 13-12-2006, 11:51 AM -
What is System balance?
By shogun7 in forum Technical SpeculationsReplies: 56Last Post: 19-01-2006, 09:47 AM -
R507 in an R134a compressor: system design
By DaBit in forum Technical SpeculationsReplies: 17Last Post: 01-05-2003, 09:25 AM