    gas change



    I am specifying a shop reform which includes new AC splits
    The existing units use 407c and we wish to leave the pipework in place. the new units (same size) use 410a

    DO we need to specify any proceedures (cleaning etc)?

    Grateful for any advice

    George



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: gas change

    Check for oil compatibility between the two systems.

    Cleaning of the pipework would be good idea anyway.

    Is pipework suitable for R410a pressures?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    gdodds's Avatar
    gdodds Guest

    Re: gas change

    I assume you are talking about compressor oil and my (limited!) understanding suggests that 407 and 410 sytems dictate similar/compatible oils anyway.
    The installers have intimated that purging the pipes with 410 will clear most of any residue and they usually do this.
    I do not want to cut corners but todays inviroment precludes contract losing overkill.
    Thank you for your promt reply to my first post
    Kind regards
    George

  4. #4
    Join Date
    Jun 2009
    Location
    East Anglia
    Age
    38
    Posts
    204
    Rep Power
    15

    Re: gas change

    Quote Originally Posted by gdodds View Post
    purging the pipes with 410 will clear most of any residue and they usually do this.



    I do not want to cut corners but todays inviroment
    How conflicting!


  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: gas change

    Quote Originally Posted by gdodds View Post
    The installers have intimated that purging the pipes with 410 will clear most of any residue and they usually do this.
    This is an illegal practice in the EU, not the sign of a good contractor.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Basics or is it?
    By Fett in forum Fundamentals
    Replies: 17
    Last Post: 10-09-2009, 01:45 AM
  2. Oil change problem
    By murray75 in forum Technical Discussions
    Replies: 2
    Last Post: 06-02-2009, 07:20 AM
  3. Change over 2 outdoor unit
    By bach in forum Air Conditioning
    Replies: 8
    Last Post: 08-06-2008, 06:55 PM
  4. Freus, water cooled, change gas?
    By Dennis Williams in forum Air Conditioning
    Replies: 2
    Last Post: 27-06-2007, 07:04 PM
  5. love to hear from the pros.(gas change)
    By jamcool in forum Refrigerants
    Replies: 9
    Last Post: 17-11-2006, 01:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •