    Lennox package coil icing up



    Hi all,

    Got to attend a unit with regards to complaints the coil is icing up. (In heating mode) Its a Lennox package Lha model,

    I dont suspect the unit to be low on gas as I serviced it not so long ago,

    Just wondering if anyone can tell me how the defrost cycle is determined on these units before I get there.

    Cheers
    Lee



  2. #2
    Join Date
    Mar 2009
    Location
    Mancheser
    Age
    41
    Posts
    55
    Rep Power
    16

    Re: Lennox package coil icing up

    Well, in this case just for anybodies future reference

    It was a pipe temperature sensor (s6) had to sense 256psig/2 degrees to send the signal to a small pcb defrost timer card, (cmc), this sending the signal out to relay (k4) this activating the heat pump solenoid every 30, 60 or 120 minutes depending on setting.

    In this case it was the defrost timer card (cmc) that happened to be faulty.

Similar Threads

  1. lennox outdoor unit icing up
    By lenboy in forum Heat Pumps
    Replies: 1
    Last Post: 13-12-2009, 07:47 AM
  2. Outdoor coil icing up...
    By airflo in forum Heat Pumps
    Replies: 18
    Last Post: 28-10-2008, 07:12 PM
  3. removing humidity
    By Sledge in forum Air Conditioning
    Replies: 31
    Last Post: 22-06-2007, 05:40 AM
  4. walk in cooler EVAPORATOR coil icing up
    By kurt854 in forum Fundamentals
    Replies: 5
    Last Post: 14-06-2007, 07:28 PM
  5. Lennox fan coil unit question
    By THERMOACC in forum Fundamentals
    Replies: 2
    Last Post: 17-02-2006, 10:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •