    Fixed orifice air conditioner not cooling down



    Hi Super techs,

    Recently replaced a maneurop compressor for a 19 Kw ducted split aircon because the exisiting comp had failed mechanically. Problem is that it does not pull down room temp.

    Used Nitrogen while soldering the drier and pressure testing. Vaccummed the system and recharged as per manfrs specs based on piping lengths. (7.1 kgs)

    (Had also weighed the charge when recovering which matched manfrs specs)

    I have the following readings:Ambient temp 33*C/Room temp 26*C

    Refrigerant R22

    Low side 68 psi
    Sat Suction t. 4*C
    Suction line t. 23*C

    Liq Line 230 psi (discharge 240 psi)
    Sat Liq t. 44*C
    Liq Line t. 41*C

    Indoor unit air on: 26.5*C
    Indoor unit air off: 18*C

    Outdoor unit air on; 33*C
    Outdoor unit air off: 41.4*C

    condensor,evaporater and filters are clean

    The suction pressure fluctuates between 60 and 75 psi approx every 30-40 seconds, and the orifice in the indoor unit makes a rattling sound during this period.

    please help me figure out what is going on here. i know the super heat and sub cooling are out of order . From my knowledge i should expect 9k superheat and 8.5k subcooling. Pls correct me if i'm wrong guys...
    Could the "accutrol" ( orifice rattling be the fault???)

    cheers



  2. #2
    Join Date
    Jan 2009
    Location
    london
    Posts
    52
    Rep Power
    16

    Re: Fixed orifice air conditioner not cooling down

    Quote Originally Posted by aquasanj View Post
    Hi Super techs,

    Recently replaced a maneurop compressor for a 19 Kw ducted split aircon because the exisiting comp had failed mechanically. Problem is that it does not pull down room temp.

    Used Nitrogen while soldering the drier and pressure testing. Vaccummed the system and recharged as per manfrs specs based on piping lengths. (7.1 kgs)

    (Had also weighed the charge when recovering which matched manfrs specs)

    I have the following readings:Ambient temp 33*C/Room temp 26*C

    Refrigerant R22

    Low side 68 psi
    Sat Suction t. 4*C
    Suction line t. 23*C

    Liq Line 230 psi (discharge 240 psi)
    Sat Liq t. 44*C
    Liq Line t. 41*C

    Indoor unit air on: 26.5*C
    Indoor unit air off: 18*C

    Outdoor unit air on; 33*C
    Outdoor unit air off: 41.4*C

    condensor,evaporater and filters are clean

    The suction pressure fluctuates between 60 and 75 psi approx every 30-40 seconds, and the orifice in the indoor unit makes a rattling sound during this period.

    please help me figure out what is going on here. i know the super heat and sub cooling are out of order . From my knowledge i should expect 9k superheat and 8.5k subcooling. Pls correct me if i'm wrong guys...
    Could the "accutrol" ( orifice rattling be the fault???)

    cheers
    Hi aquasanj,

    just a couple of questions;

    Did you re-use refrigerant?

    Is there a small in-line filter before the fixed orifice? Could there be a foriegn object there? I had a similar expierience.

    What type of control fan control do you have?

    Looking at the temp/pressures you have, it is looking short of gas.

    Could the noise be just a shortage of gas going through the orifice?

  3. #3
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Fixed orifice air conditioner not cooling down

    Sounds like a Temperzone to me.
    Add a fraction more refrigerant.
    You are getting flash gas through the orifice.

  4. #4
    Join Date
    Dec 2009
    Location
    AUSTRALIA
    Posts
    14
    Rep Power
    0

    Re: Fixed orifice air conditioner not cooling down

    Hi buddy,

    I charged virgin gas, as for the filter, i can,t tell maybe it is inside the line just before the orifice and the orifice is soldered so i may have to disconnect to check.
    The indoor fan is controlled by a wall controller and has 3 speeds. the outdoor fans (2) are fixed speed.
    I managed to note down the info i gave when it was sitting at those pressures for a short while during its fluctuating cycles.
    It may be short of gas but the liquid line is quite warm (41*C), i did think it may be short of gas but was reluctant to add more than the mnfrs specs....did not want to over heat the liquid line
    cheers

  5. #5
    Join Date
    Dec 2009
    Location
    AUSTRALIA
    Posts
    14
    Rep Power
    0

    Re: Fixed orifice air conditioner not cooling down

    Hi mate,

    Its an APAC unit, you probably heard of these.

    I could add more gas but what would happen if my liquid line heats up too much......why would the suction pressure hunt as it does between 60 and 75 psi...not much change in the head pressure though....

    cheers

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Fixed orifice air conditioner not cooling down

    Quote Originally Posted by aquasanj View Post
    Hi buddy,

    I charged virgin gas, as for the filter, i can,t tell maybe it is inside the line just before the orifice and the orifice is soldered so i may have to disconnect to check.
    The indoor fan is controlled by a wall controller and has 3 speeds. the outdoor fans (2) are fixed speed.
    I managed to note down the info i gave when it was sitting at those pressures for a short while during its fluctuating cycles.
    It may be short of gas but the liquid line is quite warm (41*C), i did think it may be short of gas but was reluctant to add more than the mnfrs specs....did not want to over heat the liquid line
    cheers
    Adding more refrigerant will cool, not heat, the liquid line.

    Add refrigerant until the superheat is right.

  7. #7
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Fixed orifice air conditioner not cooling down

    Quote Originally Posted by aquasanj View Post
    Hi mate,

    Its an APAC unit, you probably heard of these.

    I could add more gas but what would happen if my liquid line heats up too much......why would the suction pressure hunt as it does between 60 and 75 psi...not much change in the head pressure though....

    cheers
    Simply you are loosing your liquid seal at the orifice,
    some times liquid, then sometimes liquid and vapour.
    Add a little more refrigerant.

  8. #8
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Fixed orifice air conditioner not cooling down

    Quote Originally Posted by mad fridgie View Post
    Simply you are loosing your liquid seal at the orifice,
    some times liquid, then sometimes liquid and vapour.
    Add a little more refrigerant.
    With an effective SC ~ 0K for an air-cooled condenser, would you expect to be able to achieve a full liquid seal at condenser outlet?

    I wonder if perhaps the OP could have positioned the new filter-drier slightly differently to the previous one? Is it set in the correct flow direction?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  9. #9
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Fixed orifice air conditioner not cooling down

    Quote Originally Posted by desA View Post
    With an effective SC ~ 0K for an air-cooled condenser, would you expect to be able to achieve a full liquid seal at condenser outlet?

    I wonder if perhaps the OP could have positioned the new filter-drier slightly differently to the previous one? Is it set in the correct flow direction?
    He will not have consistant sub-cooling, (if any at all)
    Remember in the service world we do not use highly calibrated measuring instruments. And if they were, after a while being thrown around a service van, they will not be so much calibrated as estimated

  10. #10
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Fixed orifice air conditioner not cooling down

    ^

    I'll get back in my hole, now...
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  11. #11
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Fixed orifice air conditioner not cooling down

    Quote Originally Posted by desA View Post
    ^

    I'll get back in my hole, now...
    And i bet she better looking than mine??

  12. #12
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Fixed orifice air conditioner not cooling down

    ^ Hahaha... where the 'blush' emoticon?
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  13. #13
    Join Date
    Jan 2009
    Location
    london
    Posts
    52
    Rep Power
    16

    Re: Fixed orifice air conditioner not cooling down

    Quote Originally Posted by aquasanj View Post
    Hi mate,

    Its an APAC unit, you probably heard of these.

    I could add more gas but what would happen if my liquid line heats up too much......why would the suction pressure hunt as it does between 60 and 75 psi...not much change in the head pressure though....

    cheers
    I think the reason you are seeing the system hunt, is because everything on your system has a fixed constant - outdoor fan speed control, compressor and an orifice. If you had a tev and fan speed control, I think you would see the system run a lot more smoothly, but still short of gas.
    Also gary is right, If you imagine your hot gas running through your condenser and in to your liquid line, if the liquid line is not full it goes through the condenser too quick and does not sub cool enough.
    That is why you are only seeing 3k sub-cooling. If you add more refrigerant and you have a full liquid line, the refrigerant is backed up in the condenser a little longer, enough to be sub-cooled to a reasonable level i.e 10k. I have found that if my condensing temperature is 45*c ,I would normally have a liquid line temp of around 35*c (not always spot on, but around that)
    Hope this helps.
    Troy

  14. #14
    Join Date
    Dec 2009
    Location
    AUSTRALIA
    Posts
    14
    Rep Power
    0

    Re: Fixed orifice air conditioner not cooling down

    Thanks fellas,

    Did as per your advice and charged up 330 gms to correct the situation. Apparently whatever i reclaimed was obviously not the correct charge.

    Re measured the piping length and topped up to superheat and all seems to be well now.

    The super heat and sub cooling are obviously varying as the load changes

    Many thanks guys for all your advice,

    much appreciated

    sanjay

Similar Threads

  1. Fixed orifice woes
    By Stiff Nipples in forum Air Conditioning
    Replies: 8
    Last Post: 18-08-2009, 04:53 AM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Replies: 5
    Last Post: 14-10-2005, 06:34 PM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0