31-01-2010, 01:23 PM #1
Fixed orifice air conditioner not cooling down
Hi Super techs,
Recently replaced a maneurop compressor for a 19 Kw ducted split aircon because the exisiting comp had failed mechanically. Problem is that it does not pull down room temp.
Used Nitrogen while soldering the drier and pressure testing. Vaccummed the system and recharged as per manfrs specs based on piping lengths. (7.1 kgs)
(Had also weighed the charge when recovering which matched manfrs specs)
I have the following readings:Ambient temp 33*C/Room temp 26*C
Refrigerant R22
Low side 68 psi
Sat Suction t. 4*C
Suction line t. 23*C
Liq Line 230 psi (discharge 240 psi)
Sat Liq t. 44*C
Liq Line t. 41*C
Indoor unit air on: 26.5*C
Indoor unit air off: 18*C
Outdoor unit air on; 33*C
Outdoor unit air off: 41.4*C
condensor,evaporater and filters are clean
The suction pressure fluctuates between 60 and 75 psi approx every 30-40 seconds, and the orifice in the indoor unit makes a rattling sound during this period.
please help me figure out what is going on here. i know the super heat and sub cooling are out of order . From my knowledge i should expect 9k superheat and 8.5k subcooling. Pls correct me if i'm wrong guys...
Could the "accutrol" ( orifice rattling be the fault???)
cheers
-
31-01-2010, 06:25 PM #2
Re: Fixed orifice air conditioner not cooling down
Hi aquasanj,
just a couple of questions;
Did you re-use refrigerant?
Is there a small in-line filter before the fixed orifice? Could there be a foriegn object there? I had a similar expierience.
What type of control fan control do you have?
Looking at the temp/pressures you have, it is looking short of gas.
Could the noise be just a shortage of gas going through the orifice?
-
31-01-2010, 07:57 PM #3
Re: Fixed orifice air conditioner not cooling down
Sounds like a Temperzone to me.
Add a fraction more refrigerant.
You are getting flash gas through the orifice.
-
31-01-2010, 10:42 PM #4
Re: Fixed orifice air conditioner not cooling down
Hi buddy,
I charged virgin gas, as for the filter, i can,t tell maybe it is inside the line just before the orifice and the orifice is soldered so i may have to disconnect to check.
The indoor fan is controlled by a wall controller and has 3 speeds. the outdoor fans (2) are fixed speed.
I managed to note down the info i gave when it was sitting at those pressures for a short while during its fluctuating cycles.
It may be short of gas but the liquid line is quite warm (41*C), i did think it may be short of gas but was reluctant to add more than the mnfrs specs....did not want to over heat the liquid line
cheers
-
31-01-2010, 10:46 PM #5
Re: Fixed orifice air conditioner not cooling down
Hi mate,
Its an APAC unit, you probably heard of these.
I could add more gas but what would happen if my liquid line heats up too much......why would the suction pressure hunt as it does between 60 and 75 psi...not much change in the head pressure though....
cheers
-
31-01-2010, 10:58 PM #6
Re: Fixed orifice air conditioner not cooling down
-
31-01-2010, 11:06 PM #7
-
01-02-2010, 02:28 AM #8
Re: Fixed orifice air conditioner not cooling down
With an effective SC ~ 0K for an air-cooled condenser, would you expect to be able to achieve a full liquid seal at condenser outlet?
I wonder if perhaps the OP could have positioned the new filter-drier slightly differently to the previous one? Is it set in the correct flow direction?Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
01-02-2010, 02:57 AM #9
Re: Fixed orifice air conditioner not cooling down
-
01-02-2010, 03:02 AM #10
Re: Fixed orifice air conditioner not cooling down
^
I'll get back in my hole, now...Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
01-02-2010, 03:07 AM #11
-
01-02-2010, 03:42 AM #12
Re: Fixed orifice air conditioner not cooling down
^ Hahaha... where the 'blush' emoticon?
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
01-02-2010, 06:01 AM #13
Re: Fixed orifice air conditioner not cooling down
I think the reason you are seeing the system hunt, is because everything on your system has a fixed constant - outdoor fan speed control, compressor and an orifice. If you had a tev and fan speed control, I think you would see the system run a lot more smoothly, but still short of gas.
Also gary is right, If you imagine your hot gas running through your condenser and in to your liquid line, if the liquid line is not full it goes through the condenser too quick and does not sub cool enough.
That is why you are only seeing 3k sub-cooling. If you add more refrigerant and you have a full liquid line, the refrigerant is backed up in the condenser a little longer, enough to be sub-cooled to a reasonable level i.e 10k. I have found that if my condensing temperature is 45*c ,I would normally have a liquid line temp of around 35*c (not always spot on, but around that)
Hope this helps.
Troy
-
02-02-2010, 12:09 PM #14
Re: Fixed orifice air conditioner not cooling down
Thanks fellas,
Did as per your advice and charged up 330 gms to correct the situation. Apparently whatever i reclaimed was obviously not the correct charge.
Re measured the piping length and topped up to superheat and all seems to be well now.
The super heat and sub cooling are obviously varying as the load changes
Many thanks guys for all your advice,
much appreciated
sanjay
Similar Threads
-
Fixed orifice woes
By Stiff Nipples in forum Air ConditioningReplies: 8Last Post: 18-08-2009, 04:53 AM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
Cooling tower evaporation, blowdown, makeup and cycles
By miltbeychok in forum IndustrialReplies: 5Last Post: 14-10-2005, 06:34 PM -
Cooling tower evaporation, blowdown, makeup and cycles
By miltbeychok in forum FundamentalsReplies: 0Last Post: 13-10-2005, 05:14 AM -
PC cooling project status update + TEV questions.
By DaBit in forum Technical SpeculationsReplies: 9Last Post: 28-06-2002, 04:03 PM