    Daikin VRV 'master' set up



    Looking for some clarification on setting up the master controller.
    The system in question is a 2 pipe heat pump 'K' series serving 6 fan coils.
    At the moment, the master is located in one of the offices but the client wants the master controller to be sited in the m.d's office.
    Would I have to power down the VRV and all fan coils, then reset. Would this effectively reset the RC's and bring the system back to pre-commissioning stage or can I do some magic within the field settings

    regards,
    Jase



  2. #2
    Join Date
    Sep 2009
    Location
    Scotland
    Posts
    374
    Rep Power
    17

    Re: Daikin VRV 'master' set up

    Quote Originally Posted by Jase View Post
    Looking for some clarification on setting up the master controller.
    The system in question is a 2 pipe heat pump 'K' series serving 6 fan coils.
    At the moment, the master is located in one of the offices but the client wants the master controller to be sited in the m.d's office.
    Would I have to power down the VRV and all fan coils, then reset. Would this effectively reset the RC's and bring the system back to pre-commissioning stage or can I do some magic within the field settings

    regards,
    Jase
    Hi Jase,

    That's an easy one
    Just locate the present heat/cool master controller, hold down the mode button until mode icon flashes, if you then press the mode button once on the controller you want as the new H/C master.

  3. #3
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: Daikin VRV 'master' set up

    Quote Originally Posted by VRVIII View Post
    Hi Jase,

    That's an easy one
    Just locate the present heat/cool master controller, hold down the mode button until mode icon flashes, if you then press the mode button once on the controller you want as the new H/C master.
    Great stuff; thanks for the prompt reply VRVIII

    Jase

  4. #4
    Join Date
    Mar 2007
    Location
    France
    Posts
    237
    Rep Power
    18

    Re: Daikin VRV 'master' set up

    Quote Originally Posted by VRVIII View Post
    Hi Jase,

    That's an easy one
    Just locate the present heat/cool master controller, hold down the mode button until mode icon flashes, if you then press the mode button once on the controller you want as the new H/C master.
    Hi Jase
    If it doesn't work or if sometimes the unit "loose" master info i could give a special setting to go on
    rgds
    cool#9

  5. #5
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: Daikin VRV 'master' set up

    Quote Originally Posted by cool#9 View Post
    Hi Jase
    If it doesn't work or if sometimes the unit "loose" master info i could give a special setting to go on
    rgds
    cool#9
    Thanks for that cool#9. Not back to site yet, but if the 'swap' doesn't work then I will take you up on the special setting

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 10:01 AM
  2. Daikin AC parts from UK
    By skel00 in forum Air Conditioning
    Replies: 5
    Last Post: 05-04-2009, 01:24 PM
  3. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 07:02 AM
  4. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 09:44 PM
  5. daikin vrv on/off remote signal trouble
    By coriolan in forum Air Conditioning
    Replies: 7
    Last Post: 09-06-2007, 11:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •