    The difference between an EPR valve and a CPR valve?



    I am trying to put together a system for a cafeteria countertop which contains an fan coil air pan and a static coil cold pan. BTU requirements are 8700 @ 20*f for the air pan and 2000 @-10*f for the cold pan. A single 404A condensing unit has been requested. Solenoid valves with a pumpdown cycle controlled with Carel T-stats was the plan. Because of the temperature difference I have concerns of system balance when the larger load ,the air pan, is satisfied and the smaller coil is still calling and being overpowered by the condensing unit.
    This is what lead me to the EPR / CPR question. As I read about the use of each of these valves it seems they are nearly the same. I believe I should use an EPR on the smaller coil because the back pressure of the condensing unit will be so overpowering. Does that sound right? Obviously I have never used these valves so I have no experience to draw from.
    Also... Am I going about this the right way or does someone have a better way to accomplish this.
    And Also...is it possible to run another air pan of the same size in this same system. Yes I do know I will have to beef up the compressor which would create an even greater difference in system balance. Ken



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

  3. #3
    Join Date
    Oct 2009
    Location
    UK
    Posts
    12
    Rep Power
    0

    Re: The difference between an EPR valve and a CPR valve?

    The theory is correct that using a epr on the low side to maintain a raised suction pressure should the main counter achieve temperature but you should be careful. If the main counter cuts out and the epr on the small coil has to shut down to increase the coil pressure there is a danger that the unit could cycle on LP switch (depending on the size of the unit), also you have to make sure that there is enough gas coming back to cool the compressor.

  4. #4
    jana's Avatar
    jana Guest

    Re: The difference between an EPR valve and a CPR valve?

    The cpr will regulate back pressure to the comp, if either of the solenoids has closed off, the comp will still be ok. the lp will shut down the system when temperature is achieved. Wire in a pump out circuit to prevent the lp cycling due to pressure rise.

  5. #5
    Join Date
    Jul 2009
    Location
    Brisbane
    Age
    67
    Posts
    79
    Rep Power
    15

    Re: The difference between an EPR valve and a CPR valve?

    The difference between the two valves is the EPR valve controls the pressure at the valve inlet and the CPR valve controls the pressure at the valve outlet.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: The difference between an EPR valve and a CPR valve?

    Quote Originally Posted by kengineering View Post
    I am trying to put together a system for a cafeteria countertop which contains an fan coil air pan and a static coil cold pan. BTU requirements are 8700 @ 20*f for the air pan and 2000 @-10*f for the cold pan. A single 404A condensing unit has been requested. Solenoid valves with a pumpdown cycle controlled with Carel T-stats was the plan. Because of the temperature difference I have concerns of system balance when the larger load ,the air pan, is satisfied and the smaller coil is still calling and being overpowered by the condensing unit.
    This is what lead me to the EPR / CPR question. As I read about the use of each of these valves it seems they are nearly the same. I believe I should use an EPR on the smaller coil because the back pressure of the condensing unit will be so overpowering. Does that sound right?
    No... the EPR would go on the warmer coil.

  7. #7
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: The difference between an EPR valve and a CPR valve?

    kengineering

    Rule of thumb i was taught was to have the low temp load at least 60% and medium temp load at 40% of the condensing unit capacity,even 50/50 was hit and miss.
    i would use 2 units if i was doing it.
    Regards

  8. #8
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: The difference between an EPR valve and a CPR valve?

    EPR / CPR valves

    EPR = back pressure valve = controlling Evaporator pressure

    CPR = outlet pressure vale = controlling crank case pressure



    but it not same totally different

    If you have two systems with two diffrent temrature (Delta T in Evaporator is important to you ) with one compressor

    You should put EPR in Evaporators is working in high pressure
    (Room temperature is high) and adjust EPR with this temperature.
    EPR is controlling and adjusting delta T of Evaporator
    So compressor suction pressure does not affect that if your pressure in suction goes down it goes to close but if your pressure is higher than EPR adjust it is open completely

    CPR should adjust with maximum suction pressure load compressor can carry – safety load (about %5 to %10)
    If your pressure goes high CPR goes to close inlet gas flow to compressor
    Meanly it is for protecting compressor from over loading and ofcourse
    It protect over heating of condenser in this case and discharge pressure if your designing load in condenser is close to compressor load .
    Last edited by mbc; 05-02-2010 at 07:55 AM.

Similar Threads

  1. LEV does not open
    By Yuri B. in forum Air Conditioning
    Replies: 7
    Last Post: 19-07-2009, 02:37 PM
  2. Replies: 2
    Last Post: 06-02-2009, 07:35 PM
  3. R22 Flooded System - Trawler
    By chiefbecker in forum System Optimization
    Replies: 18
    Last Post: 07-02-2008, 11:11 PM
  4. Service Procedures For TK Scroll
    By absolute-zero in forum Transport
    Replies: 0
    Last Post: 03-02-2008, 07:42 PM
  5. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •