Results 1 to 37 of 37
    3,856
    Why are discharge lines smaller than suction lines?
    Just read a post by MarkII and i got to wondering again
    Why are they sized differently when they have the same volume of refrigerant going down them?
    Cheers Jon
    Sep 2009
    Scotland
    374
    Re: Why are discharge lines smaller than suction lines?
    Cheers Jon
    Hi Jon,
    I’d say this is due to higher pressure in discharge line = higher velocity, so basically the gas is moving faster through the smaller discharge pipe
    Nov 2006
    708
    23
    Can ya not remember Boyles law i.e. Pressure and volume being inversley proportional. Its not the same volume in the discharge line compared to the suction as it is compressed hence it has a smaller volume but the same mass.
    it being the refrigerant
    Nov 2007
    London
    461
    Quote Originally Posted by VRVIII View Post
    Hi Jon,
    I agree with VRV 3 in relation to the higher velocities iff the discharge pipe was too large the refrigerant would change state before reaching the condenser.
    The suction line will contain vapour which will require a larger CSA to ensure that there is adequate flow rate back to the compressors at lower pressures.
    Nov 2006
    708
    23
    There are loads of very knowlegable people on this forum - my guess is that Taz or gary would be some of the best to further explain
    Sep 2003
    ISRAEL
    72
    4,248
    In any system, what goes out in the discharge, comes back in the suction.
    Vapour under high pressure require less space and when the pressure drops the vapour expand and occupy larger space.
    Just as Quality wrote.
    Nov 2006
    708
    23
    Good explanation that one looking from the opposite side. as you said what goes in only comes out.
    another thought:- imagine if refrigerant entered compressor through a 1/2" pipe was compressed then was discharged through a 1/2" pipe it would only expand into the same pressure and volume as it entered the compressor, making the comprssor a vapour pump
    the smaller discharge volume/pipe simply maintains the smaller volume created by the compressor
    hope this helps
    Sep 2009
    Scotland
    374
    Quote Originally Posted by Quality View Post
    But the discharge pressure is aprox 4 x higher than suction pressure, surely this would still take up a smaller volume even though both pipes are 1/2"???
    Split Croatia
    57
    6,151
    36
    I would say because of different recommended speeds for refrigerant in these pipes.
    Suction pipe recommended speed is about 10m/s.
    Discharge pipe recommended sped is about 12m/s. Therefore, discharge pipe could be smaller.
    Aug 2009
    New Zealand
    2,554
    26
    Mass flow is the same, volume is reduced.
    At higher pressure (more dense/ heavy) you have less pressure drop through your pipe.
    Also how the oil is carried is different.
    Think of a sponge full of water (low pressure) now squeeze the sponge (high pressure) some water leaves the sponge. In our case the sponge is refrigerant and the water is oil. We want the free oil to travel with the refrigerant, this is done with velocity (speed), hence higher velocity for discharge.
    3,856
    I don't think the density would change, i think this would be linked to the discharge pressure and in turn this would be a function of the condensing temperature.
    I think it would just travel slower along the pipe.
    Aug 2009
    New Zealand
    2,554
    26
    The mass flow is the same in the suction and discharge, in the suction you have low density, in the discharge you have higher density. What density does relate directly to your working pressures and temperatures.
    If you have the same sized pipe at high density it will have a slower velocity (slow speed), what will happen is that your oil will drop out of the refrigerant. Think of an oil seperator (more to oil seps than just this), a small pipe goes into a big pipe, the velocity slows to a snails pace a large % oil falls to the bottom, the refrigerant then goes back into a small pipe and the velocity increases again, carry what ever oil is left to the next part of the system
    Sep 2009
    Scotland
    374
    Just to confuse things further it's also possible to have the discharge line larger than the suction. I.E. Condenserless chiller with long pipe run/high head/various bends.
    See below copy paste info
    Recommended gas line velocities:
    • Suction line: 4.5 to 20 m/s
    • Discharge line: 10 to 18 m/s
    Recommended liquid line velocities:
    • from condenser to receiver: < 0.5 m/s
    • from receiver to evaporator: < 1.5 m/s
    Higher gas velocities are sometimes found in relatively short suction lines on
    comfort air-conditioning or other applications where the operating time is limited
    to 4.000 hours per year or less and where low initial cost of the system is more
    important than a low operating cost.
    Industrial or commercial refrigeration applications, where the equipment runs
    most of the time, should be designed with low refrigerant velocities in order to
    obtain the most efficient compressor performance and the lowest equipment
    operating cost.
    Liquid lines from condenser to receiver should be designed for refrigerant
    velocities of 0.5 m/s or less to ensure positive gravity flow without incurring back
    up of liquid flow.
    Liquid lines from receiver to evaporator should be designed to maintain the
    refrigerant velocities below 1.5 m/s, to avoid liquid hammering when solenoids or
    other electrically operated valves are used.
    There are two methods to determine the refrigerant line sizing: by using the pipe
    graphs or by using the selection tables. Both methods are based on the Darcy-
    Weisbach formula.
    Pressure loss in hot-gas lines increases the required compressor power per unit
    of refrigeration and decreases the compressor capacity.
    Pressure drop is kept to a minimum by generously sizing the lines for low friction
    losses, but still maintaining refrigerant line velocities to entrain and carry oil along
    at all conditions.
    Pressure drop is normally designed not to exceed the equivalent of a 1 Kelvin
    change in saturation temperature. Recommended sizing tables are based on a
    0.02 K / m change in saturation temperature.
    Jul 2008
    London
    848
    P1V1=P2V2
    Sep 2009
    Scotland
    374
    Quote Originally Posted by multisync View Post
    P1V1=P2V2
    No you've got it all wrong multi,
    Head loss: Δh = λ (l / dh) (v2 / g 2)
    Friction loss: 1 / λ1/2 = -2 log [ 2.51 / (Re λ1/2) + (k / dh) / 3.72 ]
    Aug 2009
    New Zealand
    2,554
    26
    VRV, I presume you mean a chiller with a remote condenser, never seen a chiller without a condenser???
    your determining factor is velocity if oil return is required (not so true with ammonia) So for very long long pipe runs to the condenser, you either have to size your compressor to match your required pressure drops (thus change in duty) or increase the size of the condenser, to allow for the smaller TD required to condense at the lower pressure, also allowing to resize your expansion device for the smaller pressure differential. i would also suggest if you had such a long discharge line, you would also have a long liquid line This would also cause big problems if not handled correctly
    Sep 2009
    Scotland
    374
    Quote Originally Posted by mad fridgie View Post
    Hi Mad fridgie,
    Yes I was referring to a remote condenser but most manufactures class this as a condenserless model as they are selling you a chiller without a condenser.
    The information is relating to a 134A chiller and of course liquid line is also taken in to account.
    The pressure drop should be limited to prevent the formation of flashing gas in
    the liquid line or insufficient liquid pressure at the evaporator. Liquid lines are
    normally designed so that the pressure drop in the liquid line is not greater than
    that corresponding to about a 0.5 to 1 Kelvin change in saturated temperature.
    Liquid sub-cooling is the only method of overcoming the liquid line pressure loss
    to guarantee liquid at the expansion device in the evaporator. If the sub-cooling is
    insufficient, flashing will occur within the liquid line and degrade the efficiency of
    the system. The amount of sub-cooling required can be calculated.
    Aug 2009
    New Zealand
    2,554
    26
    Hi Mad fridgie,
    Hi VRV, yes just different termnology around the world.
    You must be getting this info out of a good book, or you are in the wrong Job, you should writing manuals 'training' ect
  19. #19
    Mar 2009
    KZN, South Africa
    64
    2,212
    As VRVIII correctly stated, each line in the system is sized based on:
    1. Maximum acceptable pressure-drop (either in kPa, or equivalent K);
    2. Minimum oil-carrying velocity.
    Two property references (R-134a):
    1. @ low Tc: d,d/d,s = 36.1955/18.7399 = 1.931
    2. @ high Tc: d,d/d,s = 79.4757/18.7399 = 4.241
    Mass flowrate: m' = d*Ac*v
    So : Ac = m'/(d*v)
    Let :
    Ac,s = suction line area [m2]
    Ac,d = suction line area [m2]
    (Ac,d/Ac,s) = [m',d/(d,d*v,d)]/[m',s/(d,s*v,s)]
    = (d,s*v,s)/(d,d*v,d) with same m'
    = (d,s/d,d)*(v,s/v,d)
    Now, select the (d,s/d,d)=1/(d,d/d,s) ratio required, & tolerable (v,d/v,s) [ASHRAE] & you arrive at the ratio of flow areas.
    Ac = (pi/4)*Di^2
    Where : Di = pipe ID
    Finally,
    (Di,d/Di,s) = sqrt[(d,s/d,d)*(v,s/v,d)]
    You end up with the ratio of pipe inner diameters.
    Please check my typing - done on the fly, but the logic is basic.
    Last edited by desA; 01-02-2010 at 03:04 AM. Reason: Correction of typo's... hope it's correct now
  20. #20
    Aug 2009
    New Zealand
    2,554
    26
    I put my hand up in disgust!
    I use a software and a gut feeeling (which you need when dealing with software)
    can not add 2 + 2 together without using a calculator
  21. #21
    Mar 2009
    KZN, South Africa
    64
    2,212
    Stick the equations into a spreadsheet, plug in the property values & you'll have the line sizes. It's easy, really - for single-phase fluids.
    2-phase fluids become a little more interesting...
  22. #22
    Jul 2008
    London
    848
    No surprise me being a split basher 'n all..
  23. #23
    11,025
    On a purely simple level.
    Assuming that the liquid is water and say one litre of water occupies one metre of 25mm diameter pipe.
    If you now heat the water enough to turn it into steam consider the size of pipe that needs to accommodate that volume of steam.
  24. #24
    Spencer ma.
    108
    Why are they sized differently when they have the same volume of refrigerant going down them? To keep you from piping it wrong way!
    I did here of a lad who did just that if you can believe
    I was told by the tech who found it the guy used all the right bushings wow
  25. #25
    Nov 2009
    Minsk, Belarus
    171
    15
    In addition vapour in suction pipe has high density in discharge lower. For good oil-carrying velosity in discharge pipe must be higher.
    For every 30 m of pipe.
    In some places will have to think ...
  26. #26
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by tonyhavcr View Post
    It is not same volume. It is same mass flow!
    That doesn't mean same.
  27. #27
    Nov 2009
    Minsk, Belarus
    171
    15
    Hi!
    About liquid pipe from receiver have some questions... In many literature sources liquid velocity must be 0.3-1.2 m/s.
    Cuold anybody tell physical side of minimum and maximum velocities in liquid pipe?
    I have view that liquid is sudcooling only after receiver in pipe, usually pipes situated in room with temperature of air smaller than temperature of pipe and liquid is subcooling. And velocity of 1.2 m/s of liqid don't give to appear fleshing in gorizontal pipe.
    In receiver vapor and liquid be in equilibrium. What subcolling is can be if vapor and liquid be in equilibrium?
    May be I don't understend something, could somebody explain?
  28. #28
    Split Croatia
    57
    6,151
    36
  29. #29
    Nov 2009
    Minsk, Belarus
    171
    15
    Thanks, nike!
    What about:
    Minimum velocity is more interest.
  30. #30
    Jan 2010
    Southern California
    I read a member say that the smaller discharge pipe size on a compressor is to maintain the higher gas pressure produced by the compressor. "if the lines were 1/2 " in and out the compressor would be a vapor pump".
    In my mind I would think that if the discharge line were the same size as the suction line size, it would not effect the discharge pressure, but would only effect the discharge velocity. Right?
    JP Newbie
  31. #31
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by Zpoint View Post
    Discharge pressure is condensation pressure + pressure loss in pipes and parts from condenser to compressor.
    Condensation pressure depend on saturation temperature of refrigerant in condenser, condenser TD and condenser air inlet temperature.
  32. #32
    Oct 2005
    IRAN
    878
    Hi there,
    One thing I read above is not correct.
    In refrigeration system compressor volume flow is constant (m³/hr). Compressor is running at the same speed and the cylinder capacity is the same. BUT BUT the mass flow is different according to the refrigerant density.
    mass flow (kg/s) = Density (kg/m³) x Volume flow(m³/s)
    In my opinion desA's formula and reasoning is correct.
    Even Einstein Asked Questions
  33. #33
    Split Croatia
    57
    6,151
    36
    Isn't that a fact that, when compressor works in same operating conditions, he moves same mass of refrigerant in time. If compressor is pump, than that same mass circulate all over the circuit. How pressure, temperature and volume changes thru circuit, same mass has different density.
    Only when conditions on compressor are changed we have different mass in circulation.
    That is how I see things.
  34. #34
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by Aik View Post
    Thanks, nike!
    What about:
    Minimum velocity is all about oil return. We must maintain sufficient velocity in pipes in order to ensure oil return to compressor. Certain minimum velocities for certain refrigerants and oils are for horizontal pipes and certain are for vertical pipes.
    I don't know physics of that. There are many practical guides in piping books and some software.
  35. #35
    Nov 2009
    Minsk, Belarus
    171
    15
    I mean liquid pipe, not vapor.
  36. #36
    Split Croatia
    57
    6,151
    36
    In liquid pipe your only concern is noise and pressure drop.
  37. #37
    Nov 2009
    Minsk, Belarus
    171
    15
    I also think so, and suppose that minimum velocity in liquid pipe depends by economical considerations.
  1. Multiple leaks on capillary tube and suction lines
    By keepmecool in forum Domestic
    Last Post: 19-01-2010, 12:54 PM
  2. Suction Discharge Pressure Equalises After Cut Off
    By pramodphilip in forum Trouble Shooting
    Last Post: 23-06-2008, 07:38 PM
  3. Replies: 7
    Last Post: 17-01-2008, 02:21 AM
  4. Replies: 1
    Last Post: 11-10-2006, 08:32 PM
  5. temperatures of the suction and discharge lines
    By VIXS in forum Air Conditioning
    Last Post: 17-05-2006, 07:18 AM