    Cellar cooler freezing up



    Hi.
    I have been recently called to a cellar cooler system, (below ground,) in a hotel with a Searle evaporator coupled to a Prestcold 1 HP semi, that has been installed for years but has suddenly started frosting up. The thermostat appears to operate correctly and is cycling around 12 degrees. There is no defrost cycle and the evap fan stops every cycle. The unit is fully charged, the fins are totally clean. The fan is running at the correct speed. The superheat is correct and the expansion valve is feeding the coil evenly. No one has changed the stat setting or increased the size of the room, but for some reason the coil seems to ice up solid including the suction line. There is a suction line heat exchanger which I don't think has collapsed internally. This system is on R12 and is evaporating at about -1 degrees when the room is at 12 degrees.
    Has anyone any ideas?
    I have had this happen to me before at other sites and cannot find anything wrong.
    I end up fitting a defrost clock and it solves the problem. Any suggestions would be greatly appreciated.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Cellar cooler freezing up

    Maybe a problem with the expansion device, TXV/cap line.

    Has the humidity in the cellar changed at all?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Cellar cooler freezing up

    has this happened when the outside/ambient changed,affecting the humidity the heating in the pub cranked up staff leaving door open,are the fans running all the time compressor not stopping is it a pump down system?.

  4. #4
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    59
    Posts
    2,556
    Rep Power
    26

    Re: Cellar cooler freezing up

    This is just a function of the ambient and a bit of bad luck.
    If Evap temp -1C then would not freeze up.
    Does the cellar have some other type of cooling equipment in (self contained inline cooler)
    If yes, at night when pub is busy this will be running keep the cellar warm, cellar cooling running (more than likely cycling) As the ambient is cold cond pressure is going to be low, thus the suction pressure (evap temp) is going to be low. Once it starts to freeze, then theres no stopping it, especially as the fan is turned off in the off cycle. If a defrost clock works for you, then thats OK, there are many other ways to sort the problem.

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Cellar cooler freezing up

    Quote Originally Posted by Pykester1 View Post
    There is no defrost cycle and the evap fan stops every cycle.
    The evap fan should run continuously. This defrosts the coil in the off cycle.

  6. #6
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: Cellar cooler freezing up

    it is normal on celler cooling to get yeast groth on the evaporaterfins this grows and should be cleaned off to get full cooling without frost forming this is more common in cellars which store traditional beers

  7. #7
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    425
    Rep Power
    20

    Re: Cellar cooler freezing up

    Get the evap fan to run all the time, and see what happens - should be fine.

    Andy

  8. #8
    Join Date
    Mar 2008
    Location
    Hereford
    Posts
    39
    Rep Power
    0

    Re: Cellar cooler freezing up

    Thanks for all your input. System is not on pump down. Customer does not want fan running continuously, ( it has always been that way.)
    Have replaced expansion valve and problem has not yet reccured.
    Ambient outside cellar has changed, (indoors I mean.)
    Customer's basement central heating has been off for repairs and he said it has been much colder outside the actual cellar room for the last month.
    I did think this and the expansion valve may be the problem but I was interested in other people's opinions and experiences.
    Once again, thanks for the input.

  9. #9
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    273
    Rep Power
    16

    Re: Cellar cooler freezing up

    Evap fan should run all the time,,,,

  10. #10
    Join Date
    Aug 2009
    Location
    england
    Posts
    85
    Rep Power
    15

    Re: Cellar cooler freezing up

    Quote Originally Posted by lawrence1 View Post
    Evap fan should run all the time,,,,
    i agree, with the evap fan running all the time , this will help keep the evap coil clear of ice , once the cellar has reached the required temp and the t/stat switches of the condensing unit . worth checking that the evap coil does not need cleaning . we clean loads of coils with coil cleaner . improves the way the work no end . and saves the customer money .( reduced running costs ) oh one quick thought , the beer delivery men , do they turn off the evap fan when they make the beer delivery . AND NOT TURN IT BACK ON WHEN FINISHED . ive come across this loads over the years . by the the time the publican has noticed the evap is really iced up . turning the evap motor back on will not clear it . just a thought

  11. #11
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Cellar cooler freezing up

    Door seal stuffed.

  12. #12
    Join Date
    Jun 2007
    Location
    Cyprus
    Age
    73
    Posts
    253
    Rep Power
    17

    Re: Cellar cooler freezing up

    Sedgy, yes it is normal. Coldstores including Beer cellars (and fridges) which are used to keep a product which is in effect still 'alive' and is progressing through the ripening and rotting process, is subject to bacteria from the product forming in the coldest place. In the case of beer, it is the yeast and/or hops, and can cause horrendous growth on the evap fins if left unattended. Fruit is also a major culprit and you will find a different strain of bacteria (very dry) on the fins of a greengrocer coldstore. Fresh products are also the cause of domestic FF drain lines blocking up. And lastly, be aware of the damage vinegar (acid) can do. Restaurant chefs often make up dressings and sauces, keeping them in the fridge. Some of these may contain corrosive vinegar acid which will - in time- put pinholes in the copper evap. Changed plenty of Foster and Williams evaps due to this.
    Last edited by fridge doctor; 09-02-2010 at 01:12 PM. Reason: Sorry mate, I have just re-read your post and I thought you were asking IS IT NORMAL... Anyway comment is still useful.

  13. #13
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: Cellar cooler freezing up

    ok fridge doctor,
    as you say all info is usefull.

Similar Threads

  1. NRS BeerMaster cellar cooler
    By madfriday in forum Commercial
    Replies: 13
    Last Post: 22-06-2009, 09:24 PM
  2. Quiet cellar cooler
    By multisync in forum Trouble Shooting
    Replies: 15
    Last Post: 14-08-2008, 06:13 AM
  3. Hubbard cellar cooler
    By birchy in forum Commercial
    Replies: 7
    Last Post: 06-05-2008, 11:46 PM
  4. cellar cooler fault.
    By fireblade in forum Commercial
    Replies: 12
    Last Post: 11-07-2007, 11:33 AM
  5. Searle cellar cooler control problem
    By iceman007 in forum Electrical
    Replies: 6
    Last Post: 06-07-2004, 08:57 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •